Not very convincing, I don't think anyone has answered the OP original question!

If its not so 'grey' it should be pretty obvious!
Telectrix answered correctly, 1667 ohms.
I agreed, but also said there would be nothing wrong with putting 200 ohms.

Then as usual, the thread took an interesting and most thought provoking turn, thanks mainly to @Julie.
 
Thanks all the short circuit issue been around forever on TT systems.
Now on TN Systems given that if you’ve got a high loop readings,stick a Rcd/rcbo in.
Days gone by this would not have happened
 
  • Like
Reactions: loz2754
Correct, there isn't a requirement to operate for L-N or L-L faults within any set time but 434.x does say that protection against fault current is required, to me that does mean it has to operate in a timely manner, not necessary 0.2/0.4 sec - or even 5 sec but not several mins.

My concern wouldn't really be the cable, but the consequences of the fault itself - if this is a water/rodent/whatever issue causing the fault, the likelihood is a strong arc persisting for a long time before finally being cleared some time down the line. This could cause thermal damage/fire.

Perhaps this is why the 18th amendment 2 is looking for AFD devices - just like the premature wiring collapse, caused by bad practices - instead of fitting trunking properly Mr 'Bodgeit and Scarper' (Ltd of course) just stick the double sided tape on a dusty flaking paint surface, so by the time they leave site it's already fallen off! - Result, we have to use metal cable clips et al. same here - rather than people thinking about the consequences of high loop impedance, they just assume an RCD will sort it - hence down the line we have to start adding additional devices:

Fuse/MCB - Primary protection
RCD - Additional protection
AFDD - Additional Additional protection
????? (TBA) - Additional Additional Additional protection
I'm not sure it would ever take anywhere near that long to disconnect in any healthy circuit. The OP's measured Zs of 3.79ohms has to be the earth loop, not L-N loop, or it would be ~370m long at 4mm².

There is a mention somewhere in the OSG saying that the disconnection times should be met for L-N faults, but it doesn't link to a regulation. I'll try to find where it says this. Some of the final circuits in chapter 7 are limited by short circuit, but very few. I can't understand why this is, if it is not required by regs.
 
  • Like
Reactions: Fazz711
Here it is. Chapter 7, P77. Talks about 5s for some reason:

LN.png
 
I'm not sure it would ever take anywhere near that long to disconnect in any healthy circuit. The OP's measured Zs of 3.79ohms has to be the earth loop, not L-N loop, or it would be ~370m long at 4mm².

There is a mention somewhere in the OSG saying that the disconnection times should be met for L-N faults, but it doesn't link to a regulation. I'll try to find where it says this. Some of the final circuits in chapter 7 are limited by short circuit, but very few. I can't understand why this is, if it is not required by regs.
No, I strongly suspect that the actual L-N loop would be much less than Zs in a TT as you say.

But really my point is that we shouldn't be guessing - we should be checking.

On a TNx usually the Zs is higher than the L-N loop purely because the cpc portion is 2.5/1.5× or 4/2.5x the neutral resistance, which isn't a great difference; however in TT they are vastly different, - could be orders of magnitude.

So actually using 1667 or 200 is totally irrelevant, you wouldn't be cross checking this anyway, you would be using the rcd actual tests to prove it's OK.

As for the osg saying it should meet the same disconnection times, I am not sure it does, but I am more familiar with the regs, than the osg as I don’t need it that often, so happy to be wrong.

But that is sort of what I am saying, there is no MUST disconnect, but it should disconnect within a reasonable time frame. (if that's within the same times, great)
 
Telectrix answered correctly, 1667 ohms.
I agreed, but also said there would be nothing wrong with putting 200 ohms.
Exactly my point! ....... Is it 1667 ohms or 200 ???
OR Something else??
Confusing for the OP!
 
I'm not sure it would ever take anywhere near that long to disconnect in any healthy circuit. The OP's measured Zs of 3.79ohms has to be the earth loop, not L-N loop, or it would be ~370m long at 4mm².

There is a mention somewhere in the OSG saying that the disconnection times should be met for L-N faults, but it doesn't link to a regulation. I'll try to find where it says this. Some of the final circuits in chapter 7 are limited by short circuit, but very few. I can't understand why this is, if it is not required by regs.
Cheers,yea it’s the earth loop.
 
Is it a time now that we actually do a L/N test,we always have a ZS, & automatic Psc @ that outlet.
We then can do the short circuit protection calculation.
 
  • Like
Reactions: loz2754
No, I strongly suspect that the actual L-N loop would be much less than Zs in a TT as you say.

But really my point is that we shouldn't be guessing - we should be checking.

On a TNx usually the Zs is higher than the L-N loop purely because the cpc portion is 2.5/1.5× or 4/2.5x the neutral resistance, which isn't a great difference; however in TT they are vastly different, - could be orders of magnitude.

So actually using 1667 or 200 is totally irrelevant, you wouldn't be cross checking this anyway, you would be using the rcd actual tests to prove it's OK.

As for the osg saying it should meet the same disconnection times, I am not sure it does, but I am more familiar with the regs, than the osg as I don’t need it that often, so happy to be wrong.

But that is sort of what I am saying, there is no MUST disconnect, but it should disconnect within a reasonable time frame. (if that's within the same times, great)
Agree, it should disconnect sooner rather than later. But it is a struggle to find a circuit where SC loop impedance would the limiting factor, at least for the type of work I do. Voltage drop almost always gets there first. Very lightly loaded, very long lighting circuits perhaps.

The OSG paragraph is in my previous post #24, but doesn't link to a regulation, and I can't find anything in the regs that directly back it up.
 
  • Like
Reactions: loz2754
Is it a time now that we actually do a L/N test,we always have a ZS, & automatic Psc @ that outlet.
We then can do the short circuit protection calculation.
On TT yes, I believe so.

In my opinion this should replace the earth fault loop test/calculations, as earth fault is covered by testing the rcd.

On TNx, not required, the earth fault loop covers it, if the rcd is additional protection

BUT, if the rcd is applied to the TNx because the earth fault loop cannot meet the disconnection time, then I think both sets of loops/calculations are needed.
 
  • Like
  • Agree
Reactions: pc1966 and loz2754
Agree, it should disconnect sooner rather than later. But it is a struggle to find a circuit where SC loop impedance would the limiting factor, at least for the type of work I do. Voltage drop almost always gets there first. Very lightly loaded, very long lighting circuits perhaps.

The OSG paragraph is in my previous post #24, but doesn't link to a regulation, and I can't find anything in the regs that directly back it up.
Well I actually dug my osg out last night, dusted it off and cleaned the cobwebs away, and yes it's in there!

That note and looking at the table suggests the loop impedance is the most common limiting factor without a rcd, and my experience would be the same, although the only real occasion in my experience is long remote lighting with small loads.

I don't know of a regulation which determines a required trip time, but obviously there's a subsection for fault protection which doesn't seperate a need between line-line, line-neutral, or live-cpc/earth, basically demanding protection for all types of fault current, whist live-cpc/earth faults do have a specific set of disconnection times
 
  • Like
Reactions: pc1966 and loz2754
Well I actually dug my osg out last night, dusted it off and cleaned the cobwebs away, and yes it's in there!

That note and looking at the table suggests the loop impedance is the most common limiting factor without a rcd, and my experience would be the same, although the only real occasion in my experience is long remote lighting with small loads.

I don't know of a regulation which determines a required trip time, but obviously there's a subsection for fault protection which doesn't seperate a need between line-line, line-neutral, or live-cpc/earth, basically demanding protection for all types of fault current, whist live-cpc/earth faults do have a specific set of disconnection times
Just thinking out loud:

434.5.2
A fault occurring at any point in a circuit shall be interrupted within a time such that the fault current does not cause the permitted limiting temperature of any conductor or cable to be exceeded.

it then goes on to give a rearrangement of the adiabatic to calculate that time. The adiabatic is only accurate for faults lasting up to 5 seconds. Perhaps this is why the OSG wants us to limit the duration of any fault to 5s?
 
Zs is measured to determine whether or not fault protection is achieved. The requirements for fault protection do not concern themselves in any way, shape or form with short circuit protection.

Section 434 is where you will find the requirements for disconnection under short circuit conditions.

To answer the OP's original question, 1667 ohms is the correct value as the sole means of fault protection is the 30mA RCD. If stable TN values have been achieved then the correct value to input would be 7667 ohms.
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Just wondering
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
32

Thread Tags

Tags Tags
wondering

Advert

Thread statistics

Created
cliffed,
Last reply from
D Skelton,
Replies
32
Views
4,630

Advert