a problem with 11kw motor.
needs a 15kw star/delta starter have got
overload contacts rated 18-24amps
motor start up in star 20.4 amps
running in delta 11.8 amps

the manufacturer has told me that it is a beast to start due to the high currents needed , they suggest fuses, a bit difficult as all distribution boards are circuit breakers. allowing for 6x start up current, can anyone suggest what rating circuit breaker and what type to use
 
Not sure if understand your exact setup here. The overload needs to be set closer to the run current. An overload set at 18A with a run current of 11.8A leaves the motor wide open to overload damage.

Your question about the circuit breaker I would suggest that the MCB would be appropriately sized for the cable it's supplying, not for the load being driven.
 
o.k. so the overload to be set at 11.8 amps, not a problem
at the moment 4.0mm 3core armoured on a 32amp triple pole type c mcb cannot hold it in. after calculating the size of cable through a software porgramme, there didn't seem to be an issue with the size of cable
 
i was thinking of a 32amp type d triple pole mcb (merlin gerin)
i had a similar problem with a three phase compressor (again no help from the supplier and manufacturer!)
 
I would also imagine a 32A D-curve MCB would be fine in this application.

If the motor is dirving a fairly constant load I wouldn't be afraid to check the actual running current with a clamp meter and set the thermal overload even lower the calculated 11.8 Amps if you can. I tend to err on the side of caution and set them as close as possible.

I also try to spec the thermal so the setting is toward the upper end of it's range that way if some muppet twiddles with it there's still a good chance it will do its job even on its highest setting. In this case I would go with a 7-13A overload rather than one with a range of 11-16A for example.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
KWh Calculation
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
ratheepkrk,
Last reply from
Marvo,
Replies
14
Views
3,101

Advert

Back
Top