Do you know that the T&E is buried at a depth of less than 50mm?

Maybe you can see that it is, or maybe you're guessing?

I had a similar situation recently. As far as I could see it looked like the cable was always over 50mm deep in the wall, but I couldn't inspect the whole run.

I didn't code it, but listed it in the limitations. You'd hope that the people who installed it 5 years ago would've done it properly...
 
With tt anyhow
With tncs or tns yes its additional... but it's still a requirement really unless someone can show me something that says different.

It is a requirement. So is brown sleeving on black cables that are live. Does not make it potentially dangerous if it is missing though does it.
 
Is the buried at less than 50mm rule still apply to cables within the prescribed zones?
 
For me right now .
Both.
But I'm willing to be persuaded otherwise .. but I'm not yet.
Yes in the case of TT then it's different. Like I said my argument is solely for buried twin and earth cables less than 50mm deep.
 
Just thinking out loud - if the TT was PME’d then at least the sub-main would have fault protection. I did a job recently where SSE had just been through and upgraded the o/h and were able to provide PME.
 
Would there be much point putting a 100ma RCD upfront of one of these sub mains as it still wouldnt meet the 30ma requirement?

in my opinion it would be worth it, especially if it was me that had just put a nail through the cable.
 