Discuss LED downlights dim when kettle switched on.. in the Lighting Forum area at ElectriciansForums.net
Haven't seen this one before.. a string of 8 dimmable downlights in the lounge (max total load 40W) on a Hamilton LED dimmer ((LED-IT B) dim slightly when a decent load is switched on eg kettle. Then goes bright again when load off. Dimmer works fine on its own knob..
New build house, wired and tested by myself, different rcbo circuits.
Can anyone explain why/how this can happen!?
I haven't done many trials of which loads and circuits do it but I'm going back in a couple of weeks to do other work too, maybe try change the dimmer module?
I dont think any other rooms do it but not many are on dimmers. There are 3 outside lamps on the other dimmer switch next to the offending one and these seem ok..
I would check the incoming voltage under load.
What is the PSSC at the incoming board?
LEDs are usually less sensitive to volts than filament lamps are, but no idea if some dodgy dimmer might amplify and changes.
Best case is it is just down to a high supply impedance at the end of a long DNO cable.
Worst case is a bad joint somewhere as that could become a fire hazard.
I would have to dig out the paperwork but I if i remember correctly it was around 2kA.
2kA is a fairly stiff supply, a 13A load would only cause about 1.5V change which is well under 1% and unlikely to be noticeable on LEDs.
I would be checking for any loose connections or changes in the supply characteristics.
Have they recently had a smart meter fitted or similar?
if some dodgy dimmer might amplify any changes.
This. Some combinations of 230V dimmer and LED are ridiculously sensitive to both voltage variations and waveform distortion. They might give a reasonable impression of dimming smoothly, but interact with each other and with other loads.
For example, we put some into one of our mobile units, they worked fine on normal mains, but when running on a good sized genny (100kVA) putting out a reasonably steady 230V they were all over the shop, bright, dark, sometimes flashing on and off. Changed the dimmers to a different flavour, this time they weren't doing anything crazy by themselves but started dimming unacceptably when the aircon or projectors fired up, even though the voltage drop was reasonably within spec.
Not sure there is any reliable way to validate a pairing of lights and dimmers without thorough testing and experience of the products.
they did have the solar pv guys in connecting the panels, since I did the installation testing..
Reply to LED downlights dim when kettle switched on.. in the Lighting Forum area at ElectriciansForums.net
I have a led panel that i want to dim. It is dimmable but without a dimmable driver. I have a dimmer module and a dimmer switch as shown in the...
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...