truckster

Am I having a brain fart?? I fitted 4no. two gang sockets fed from a 5A fuse in a shop for display lighting. The shop fitters arrived some time later and fitted a bunch of LED lights. Each driver states input as 1.2 amps and there are sixteen of them?? However each driver is only supplying about 10-16 watts of LEDS. 1.3A at 12v. so around .06A at 240V yet they are blowing a 5A fuse? Jesus I need a holiday!!
 
you sure your not getting input and output mixed up? seems to me that the transformers pull 1.2 amps each
 
What's the Clamped current?
Or don't they stay on long enough?

Do they work with only 1 driver at a time plugged in?
Has someone also got a 110v transformer plugged into one of the sockets?
 
Had a couple of drivers in the past where they had labeled up the output and input wrong so could be worth checking the drivers have been installed the right way round 230 volts down the 12 volt output will certainly blow the fuse
 
Had a couple of drivers in the past where they had labeled up the output and input wrong so could be worth checking the drivers have been installed the right way round 230 volts down the 12 volt output will certainly blow the fuse


Thanks guys, got to go back and check the input/outputs will clamp it and see.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Led drivers brain fart
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
truckster,
Last reply from
truckster,
Replies
5
Views
1,394

Advert