I have a light switch where the CPC has been used for a lighting circuit and sleeved. Previously I would give this a C3 (411.3.1.1) and leave a sticker on the Consumer Unit to advise no CPC at accessory, only use class II accessories. However, the CPC from another switch the other side of the wall has been used to earth the back box. Does this now negate the sticker, but still code as C3 ?
I recall Amd 2, now makes it unacceptable to use CPC in any circumstances, does anyone recall the regulation, and what code would you now give this?
 
I have a light switch where the CPC has been used for a lighting circuit and sleeved. Previously I would give this a C3 (411.3.1.1) and leave a sticker on the Consumer Unit to advise no CPC at accessory, only use class II accessories. However, the CPC from another switch the other side of the wall has been used to earth the back box. Does this now negate the sticker, but still code as C3 ?
I recall Amd 2, now makes it unacceptable to use CPC in any circumstances, does anyone recall the regulation, and what code would you now give this?

I'm not sure much has changed in the situation you are looking at, assuming that it's a twin and earth install.

The bare cpc conductor in a twin and earth was never acceptable to use as a live core, because it isn't insulated along its length. sleeving at one end doesn't fix that.

If it were a flex cable, with an insulated g/y core, then that was commonly over sleeved in brown at the terminations, particularly by heating engineers or in boiler applications.

The regs only require a cpc to be provided at every accessory. Assuming the accessory is Class 2, then it being missing I'd only ever code as a C3. And I've used the same stickers. That was the guidance for a while when changing consumer units with old lighting cables without cpc.

There is also reg 543.6.1:

"Where overcurrent protective devices are used for fault protection, the protective conductor shall be incorporated in the same wiring system as the live conductors or in their immediate proximity."​

But in your case, the cpc for an adjacent light switch would meet that. Is it on the same circuit? If so, then no code at all for earthing.

So the main issue then is how to code a cpc being used as live (presumably a 2 way lighting install?)

If it's twin and earth, I'd be veering towards C2, though if there was RCD protection throughout, a C3 might not be impossible. Obviously if anyone broke into that cable half way they would expect the bare cpc to be earthed, and all sorts of problems could follow....

If it was flex, so sheathed earth then sleeved at the end, I'd go C3.

Edit:

Found the reg re protective conductors:

514.4.2
Protective conductor
The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor and this combination shall not be used for any other purpose. In this combination one of the colours shall cover at least 30 % and at most 70 % of the surface being coloured, while the other colour shall cover the remainder of the surface.

Single-core cables identified by green-and-yellow throughout their length shall only be used as a protective conductor and shall not be overmarked at their terminations, except as permitted by Regulation 514.4.3.

A bare conductor or busbar used as a protective conductor shall be identified, where necessary, by equal green-and-yellow stripes, each not less than 15 mm and not more than 100 mm wide, close together, either throughout the length of the conductor or in each compartment and unit and at each accessible position.

(514.4.3 is for PEN conductors, so not applicable within domestic installs)
 
CPC-as-live sounds pretty dangerous to me. Can potentially result in all sorts of shenanigans if it's also marked as earth in other accessories. Deffo C2 at a minimum. For me it's not quite a C1 as it's not an immediate danger but it has the potential to be very dangerous. It's like a C2 1/2.
 
CPC-as-live sounds pretty dangerous to me. Can potentially result in all sorts of shenanigans if it's also marked as earth in other accessories. Deffo C2 at a minimum. For me it's not quite a C1 as it's not an immediate danger but it has the potential to be very dangerous. It's like a C2 1/2.
Surely you mean a C1½ as a C2½ is nearly a C3
 
Simplest solution would be to isolate the 2 way bit and then use Quinetic switches if they are desperate for it - that's assuming there isn't a borrowed neutral, or other dodgy wiring tricks used by whoever connected it up that way....
 

Reply to Lighting accessory borrowed CPC code. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
513
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock