electricalrob

Hi there don't know if anyone can help. but I had a strange lighting fault none of the lights where working but 240v coming out of the mcb so I checked the first fitting and it was saying there was only 12v there and every fitting I checked had this. there are no transformers on the circuit so im a bit baffled going back monday to check every leg of the circuit. Lights do come on but only one will and if you put a second on the first one goes off.
Cheers
Rob
 
Lost your neutral?
When you say 12v are you measuring to neutral? Have you tried to earth?

Boydy
 
Thanks for getting back. I was thinking lost neutral i couldnt measure to earth because it takes out the rcd but usually when i've had a lost neutral it says 50v or something along them lines.


Rob
 
Thanks for getting back. I was thinking lost neutral i couldnt measure to earth because it takes out the rcd but usually when i've had a lost neutral it says 50v or something along them lines.


Rob
If you disconnect the supply from the RCD you can test the neutral to earth and phase to earth regarding continuity though surely Gasp, Help Help is it Friday or am I feeling ill,
 
Yeah disconnecting the RCD was my next step i didn't get a chance this morning will do monday i think i will just have to work through the circuit and find the fault just wondered if anyone had seen this before just something i never have come across.
 
So, get your wander lead out and check the continuity of the live, neutral and cpc at light one. Then at light two.

Time to go back to basics!
 
Yeah Thnks for everyones help I knew i had to go back to basics I just wanted to see if anyone had came across this fault. I remember why I try to keep away for domestic jobs I only got signed up to this because it was my wifes friend
 
It's always best to include photos with your question as it makes it much easier to......................................see what she looks like, nice?

Boydy
 
Yeah Thnks for everyones help I knew i had to go back to basics I just wanted to see if anyone had came across this fault. I remember why I try to keep away for domestic jobs I only got signed up to this because it was my wifes friend

This type of fault could happen in any area of sparking .........
 
Thats true but I don't mind working on in it work. But its when im there in my spare time and I didnt want to be there anyways and i can't chanrge that much because its my wifes friend.
 
easy method. power off the circuit. connect meter ( on ohms) to L and N of the light circuit in CU. switch on lights 1 at a time. if circuit is healthy to any fitting, then you will read the resistance of the lamp.
 