D
davesparks
Immediate thoughts were;
131.7 Protection against power supply interruption
Where danger or damage is expected to arise due to an interruption of supply, suitable provisions shall be made int he installation or installed equipment.
132.10 Disconnecting devices
Disconnecting devices shall be provided so as to permit switching and/or isolation of the electrical installation,circuits or individual items of equipment as required for operation, inspection, testing, fault detection, maintenance and repair.
132.15.201
Effective means, suitably placed for ready operation, shall be provided so that all voltage may be cutoff from every installation, from every circuit thereof and from all equipment, as may be necessary to prevent or remove danger.
134.1.1
Good workmanship by one or more skilled or instructed persons and proper materials shall be used in
the erection of the electrical installation. The installation of electrical equipment shall take account of manufacturers'
instructions.
Fundamentally non-compliant, would say C3 but would push for C2 depending if the lighting is on the boiler circuit or boiler on lighting circuit. If your boiler doesn't work your lighting won't come on so could be argued potentially dangerous (as would not be immediate where the fault lie, whereas if your lighting works but your boiler doesn't, I wouldn't give it the same gravity.
The only one of those you can really use is good workmanship.