When I came to testing on of the ring finals in the house, when testing insulation resistance the live and earth legs on the ring are clear but live to the earth on cpc’s on the cooker circuit, other ring, downstairs lights and heating its bang down I’m thinking something to do with damp walls? But every time Other circuit tested out fine on IR
 
What I meant was if for say the cooker circuit you did:
L to N and got >999mohms
N to E and got >999mohms
And L to E gave 0mohms

then you can be pretty sure there’s a dead short somewhere as
1) any dampness would not cause zero anyway
2) any dampness would be unlikely to affect just one core

So I would then use the (low resistance) continuity function to measure more accurately what the resistance is between L and E. That can then give you some idea where the fault is.

As there’s a rfc affected, if you take both ends out of CU and measure L to E on continuity at the sockets the resistance should drop as you get nearer the fault and the fault will be between the two lowest readings.

It interesting that so many circuits are apparently affected. Forgive the silly question but are you testing in the top of the breakers and are the breakers all off?
 
What I meant was if for say the cooker circuit you did:
L to N and got >999mohms
N to E and got >999mohms
And L to E gave 0mohms

then you can be pretty sure there’s a dead short somewhere as
1) any dampness would not cause zero anyway
2) any dampness would be unlikely to affect just one core

So I would then use the (low resistance) continuity function to measure more accurately what the resistance is between L and E. That can then give you some idea where the fault is.

As there’s a rfc affected, if you take both ends out of CU and measure L to E on continuity at the sockets the resistance should drop as you get nearer the fault and the fault will be between the two lowest readings.

It interesting that so many circuits are apparently affected. Forgive the silly question but are you testing in the top of the breakers and are the breakers all off?
For the cooker circuit all tests are clear including L-E the only one that’s down is L on the sockets the other cps I was disconnecting the cpcs one at a time from earth bar
For example
Clip on L from sockets circuit then clipping onto cpc for cooker that’s down
 
What I meant was if for say the cooker circuit you did:
L to N and got >999mohms
N to E and got >999mohms
And L to E gave 0mohms

then you can be pretty sure there’s a dead short somewhere as
1) any dampness would not cause zero anyway
2) any dampness would be unlikely to affect just one core

So I would then use the (low resistance) continuity function to measure more accurately what the resistance is between L and E. That can then give you some idea where the fault is.

As there’s a rfc affected, if you take both ends out of CU and measure L to E on continuity at the sockets the resistance should drop as you get nearer the fault and the fault will be between the two lowest readings.

It interesting that so many circuits are apparently affected. Forgive the silly question but are you testing in the top of the breakers and are the breakers all off?
All breakers off just in the top individually testing them to earth
 
Basically 0 M ohm

So was testing a house today (new build)
When I came to testing on of the ring finals in the house, when testing insulation resistance the live and earth legs on the ring are clear but live to the earth on cpc’s on the cooker circuit, other ring, downstairs lights and heating its bang down I’m thinking something to do with damp walls? But every time Other circuit tested out fine on IR
Are all the conductors under test dissed from the CU INCLUDING THE MAIN EARTH During testing?
 
For the cooker circuit all tests are clear including L-E the only one that’s down is L on the sockets the other cps I was disconnecting the cpcs one at a time from earth bar
For example
Clip on L from sockets circuit then clipping onto cpc for cooker that’s down
Normally you IR test with all CPC connected to the MET so a fault from, say, L to some wet brickwork will appear. Only then would you remove the CPC for that circuit to try and find out if the fault is L-CPC or L-Earth somewhere.

I see @Pete999 just posted about that!
 
Normally you IR test with all CPC connected to the MET so a fault from, say, L to some wet brickwork will appear. Only then would you remove the CPC for that circuit to try and find out if the fault is L-CPC or L-Earth somewhere.

I see @Pete999 just posted about that!
They was all connected to start with then I started disconnecting some then still testing via the MET to see which cpcs were bringing it down
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Retford
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Live earth fault??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
Kyle_Trainee,
Last reply from
timhoward,
Replies
29
Views
7,485

Advert

Back
Top