The Ghost

Went to daughters house to replace a couple of broken sockets and did a Zs and RCD test after replacing. CU was replaced and notice on it said inspected 2015. Plastic dual RCD 30 ma/Main switch 60947-3 isolator. System is TT. (100ma RCD?)
Zs at socket was 11.75 ohms L-PE 2.64 ohms L-N. No bonding present to services. Suggested my daughter might get the council in to check it out. Had a phone call today and electrician said it is all compliant! He also said it disconnects in 0.37ms and I asked to talk to him he would not. He said I was just trying to make money, if only he knew? Apparently he fixed the bonding in a few minutes.
I said to my daughter tell him it should be 0.2 (the property is not cross bonded as in the exception to table 41.1) he said that was the case 20 years ago and I needed to get up to date. Okay!
I must confess to be a little bit taken aback by this and thought I would do a sanity check with the forum members. I do have Amd 3 BS7671 by the way i.e. 2382-15 so I think I am up to date.
Essentially I am of course concerned for my daughter, and what appears to be possibly a cavalier attitude. I told my daughter to get a copy of the report and tests so we await that. Am I being concerned over nothing or just plain stupid??? Tin hat on.
 
The 0.37mS time for the RCD would comply at both 1x and 5xIn so would pass.

As for plastic board in 2015 all depends on when the installation was designed, might be the council has a generic design for those properties.
 
  • Agree
Reactions: buzzlightyear
Ive been told that 100ma isnt sufficient enough now amd that it needs to be 30ma. If its a tt system surely the zs at the socket is ok??
 
considering it could be council proprty ,then your daughter should contact them .and rectify the damaged sockets .not you Vort .you had no write to do such work unless you have their writen consent.
 
  • Agree
Reactions: 1 person
0.37ms, that is quick what meter did he have.

Beaten to it:(
 
The rcds are providing fault protection so the only issue is bonding??
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Looking for opinion on whether this scenario is compliant
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
55

Advert

Thread statistics

Created
The Ghost,
Last reply from
rompling,
Replies
55
Views
5,396

Advert