I tested a tt system yestersay and the zs at db was 9.11 ohms with ipf of 25a, on the socket circuit i got a zs of 10 ohms and an r1+r2 reading of 0.49 ohms and was told this was fine....i always thought and was taught a tt would give higher readings for a zs than as given in appendix table b6. Now im confused 