RodLinin

This is my first post and I hope I explain it correctly/ Simply. 1100sq foot single family home, 100 amp service. I am having an electrician replace the front part of my service entrance from the weather head to the meter socket. The main panel was updated about 10 years ago and is not in need of replacement.
The grounding paths are currently this:
-Green screw correctly bonding neutral bar to the box.
-#6 bare running continuously (no splices) outside to 2 rods about 7 feet apart.
-#6 bare that runs to the water pipe right as it enters through the basement wall.
-#6 bare short jumper across the water meter.

The electrician estimating the job said that the #6 from the box to the water pipe needs to be replaced because it now has to be a continuous wire through a clamp at the water pipe entrance and then across the meter. He said “a lot changed in the nec2020. Is he correct or does the jumper wire still satisfy? I hate to think he's adding unnecessary work but I don't want to question him unless I can cite my case.
 
I think this is one for @Megawatt ...

He's the American expert
 
This is my first post and I hope I explain it correctly/ Simply. 1100sq foot single family home, 100 amp service. I am having an electrician replace the front part of my service entrance from the weather head to the meter socket. The main panel was updated about 10 years ago and is not in need of replacement.
The grounding paths are currently this:
-Green screw correctly bonding neutral bar to the box.
-#6 bare running continuously (no splices) outside to 2 rods about 7 feet apart.
-#6 bare that runs to the water pipe right as it enters through the basement wall.
-#6 bare short jumper across the water meter.

The electrician estimating the job said that the #6 from the box to the water pipe needs to be replaced because it now has to be a continuous wire through a clamp at the water pipe entrance and then across the meter. He said “a lot changed in the nec2020. Is he correct or does the jumper wire still satisfy? I hate to think he's adding unnecessary work but I don't want to question him unless I can cite my case.
You can splice at the first or second ground rod but you will need an extra tear drop or acorn for a 5/8 ground rod. You are allowed only on wire per acorn. You have to bond metal piping
 
  • Informative
Reactions: Jim_e_Jib

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Water pipe/ meter ground
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
RodLinin,
Last reply from
Megawatt,
Replies
2
Views
1,169

Advert