Discuss Looking for opinion on whether this scenario is compliant in the UK Electrical Forum area at ElectriciansForums.net

Hi - agree.
But any L-E faults before the CU's RCDs will have to clear via the service fuse. And with TT its likely it won't clear and there's risk the installation E could rise. Case of L tail flapping about inside AMD3 CU for example (very unlikely and why tails glands and good workmanship always needed).
 
Hi - agree.
But any L-E faults before the CU's RCDs will have to clear via the service fuse. And with TT its likely it won't clear and there's risk the installation E could rise. Case of L tail flapping about inside AMD3 CU for example (very unlikely and why tails glands and good workmanship always needed).
I like to install an S type rcd rather than the main switch if using a dual rcd board but that’s just my preference on TT arrangements.
 
This is a plastic CU doesn't need a 100ma main switch. The rcds in situ provide additional and fault protection as already stated.
 
Yes agreed a plastic consumer unit takes the danger scenario of loose tails touching the enclosure causing a potential hazard, out of the equation
 
Yes agreed a plastic consumer unit takes the danger scenario of loose tails touching the enclosure causing a potential hazard, out of the equation
... Although of course there's still the risk of the CU catching fire.
I had a quick leaf through the new OSG in the wholesalers the other day - there's bit in it about countering precisely that situation, but I can't remember the exact details.
 
The higher zs is fine, and dealt with by the application of rcds for fault protection, and in this case since they are 30ma they will also provide additional protection. The curve ball is the 2.64 ohm L-N....generally we assume that if R1+R2 is good then R1+RN would be as well....since the CSA of cpc will be less than or equal to the neutral...but ring finals aside, what specific tests are mandated to check this? Could well be a loose neutral connection, but how are these tested?
Often hear circumstantial evidence that it's always neutrals that burn out or are loose....is it because a loose l or cpc gets picked up during r1+r2 testing, but those pesky neutrals fall by the wayside? Just a thought....

Totally agree
 
New posts

Reply to Looking for opinion on whether this scenario is compliant in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
908
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
I'm having a bit of a disaster at the minute and would like an honest opinion. I am having a gas stove fitted in the corner of my room and...
Replies
6
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
904
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock