Hi all new to this forum site and a fairly green sparky. Need a bit of advice hope some1 can help, OK got stacked consumer units to change (main one and an economy 7 smaller one) main earth from supply side only goes to main consumer unit (16mm) and then a 10mm is just dropped down from main unit to smaller one but they both have sepertate meter tails. Please can anyone tell me if this meets 17th regs as i cannot seem to find it in there anywhere. I beleive that i should chenge the 10mm to 16mm but still do not know if linking the consumer units like this is OK. Or does the smaller unit need it's own main earth from supply side. Helppppppp. I am aware that i could put it all on one unit with seperate main switches but job is to just change them as they are.
 
Hi and welcome to the forums.

As a rule if a DB has seperate meter tails, then I would install a seperate earth aswell.

Cheers.
 
Agree with Leonard.

16mm main earth from cutout to MET. 16mm from MET to each CU.

Dont forget this work would also need notifying under Part P of the building regs.
 

Reply to Main Earth Regs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
678
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
641
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
680
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
760

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock