Hello
Looking for advise please.
Our mains RCD switch 60A 30mA MK LN 5760 is tripping when either one of my larger mcbs is turned on.
- 32A shower
- 30A sockets
- 30A cooker
I turned every breaker off and individually turned them on. All three mentioned above individually trip the mains RCD.
 
Initially I would be considering an RCD trip test and thereafter, if that was OK, an insulation resistance test individually on each circuit.
Any electrician attending a job should have a tester to do these tests.
Sorry should have mentioned the relative in the industrial trade would probably have to borrow any test equipment needed.
Thank you for your help
 
Initially I would be considering an RCD trip test and thereafter, if that was OK, an insulation resistance test individually on each circuit.
Any electrician attending a job should have a tester to do these tests.
Sorry should have mentioned the relative in the industrial trade would probably have to borrow any test equipment needed.
Thank you for your help
 
Your relative should be able to open the consumer unit,disconnect all the circuit neutrals,check the resetting of the Rcd
If it now resets,the neutral conductors can be replaced one at a time to see if balance is maintained
If he is an electrician (of whatever discipline)and have test meters,the problem should be easy to identify
 
Your relative should be able to open the consumer unit,disconnect all the circuit neutrals,check the resetting of the Rcd
If it now resets,the neutral conductors can be replaced one at a time to see if balance is maintained
If he is an electrician (of whatever discipline)and have test meters,the problem should be easy to identify
Brilliant, thank you very much :)
 
Really appreciate the response I've received from this, great group.
I'll try the advise given to see if we can individually identify something.
My relative is a electrician but unfortunately in the industrial trade.
I reckon they would be willing to have a look at it for me, is there any type of tester I could advise them bring along with them.
Failing that, looks like I will be contacting a local sparky as mentioned I've noticed the RCD not easy to get a like for like now.
Thank you
If the relative you speak of is an Electrician, he/she must be able to sort this fault out for you, after all he.she is an Electrician
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Derbyshire

Thread Information

Title
Mains RCD tripping on larger MCB's
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
Linksy5,
Last reply from
SparkyChick,
Replies
27
Views
4,272

Advert

Back
Top