100W x 13 / 230V is ~ 5.7A. But the OSG recommends max 66% diversity for a domestic lighting circuit so you can go up to 9A or 2070W which is over 20 lights! I think the 100W minimum is a bit of a relic from the days when all people had was plain bayonet cap pendants with incandescent light bulbs. Now you can have everything from a 4W LED to a 400W halogen floodlight and everything in between. So you have to work out what is likely to be fitted. I think the same would go for your 5A sockets - if you fitted 2, and they both had 5A loads frequently, that will be tripping the 6A breaker all the time, without any lights even being on! So think about what they are likely to be used for. That is my humble opinion anyway!
If you are talking about using 5A sockets solely for table and lamp standards, then yes use the 100W rule of thumb for your calculation basis!!
I used to use the old 2A socket outlets for table lamps and the like. used them in both my parents and my sister house rewires. One circuit downstairs for lounge and dining room and one circuit upstairs for the bedrooms. Switched at the normal light switch positions via a 2 or 3 gang wall switch and in the bedrooms, with two way switching by the beds......
Common sense. What he said
Reply to Max number sockets in the UK Electrical Forum area at ElectriciansForums.net
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...