I think you may need to consult the manufaturers for any applicable info as it's not in the regs.

A quick google may throw up some tech info for you.
 
You are always safer using manufacturers data on these devices, many have adjustable characteristics on the curve.


Exactly!! .... The data sheet that comes with these MCCBs will generally give you this information. If it doesn't, then it will direct you to a web site page that does. Generally all MCCBs will have different Max Zs even those of the same manufacturer, between different model numbers in the same frame size....
 
im struugling to find max zs readings for siemens breakers if anyone could help, cheers

Struggle no more, contact Siemens with the exact MCCB details, and they will furnish you with the information!!!

As i have stated above, Even MCCB's of the same manufacturer and frame size will/can have very different Max Zs requirements...
 
Amtech have a handy device called "single cable" which has almost all MCCB max Zs values for anyone that is interested

Interesting!! ...Any chance of showing a list of Schneider MCCB's with their max Zs values. I'll check them against my home made data base. ...Iv'e a feeling this list isn't going to be too accurate to be honest!!
 
Its not in simple tabulated layout form its has selection process where you choose the make, family, type, protection and rating then it calculates it for you. But if you have yours in tabulated form i'll happily check them against what amtech says.
 
you mean its not precise to 4 decimal places ??
tut tut , next you'll be rounding pi down to 3
;-D

You may scoff, but there are significant differences in MCCB maximum Zs values attached to different types, even within the same type and frame sizes and families of the same manufacturer. Were not talking about type tested MCB's here... lol!!
 

Reply to mccb max Zs ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top