Hi all,

Just after a bit of advice from all you domestic installers out there.

I've been asked to do a job in a house which involves running a cable in a wall. The cable needs to run vertical the entire height of the wall. However I cannot run it where the walls meet at an angle due to obstructions. This wall is at the base of stairs so quite small.

Can I utilise the thermostate as an acessory and run behind it (obviously taking it off wall and mounting back on after filled) to fullfill the requirementof running to an accessory. Or is this not allowed as it isn't actually supplying the accessory.

If not can I just cap the cable with metal capping at least 3mm thick. I know meeting the requirement to prevent nail penetration is hard to meet.

The circuit is covered by a 30ma rcd. Just a little confused as my domestic regs knowledge is not up to scratch. Don't want to install a cable unsafeley.

Any advice would be appreciated. Thanks
 
the thermostat is an accessory and assuming it has a LV supply, then it can serve as a pointer for a prescribed zone. won't do if it's a wireless stast.
 
It's definitely Lv. There's surface trunking supplying it. Was even thinking I could bury these supply cables as well If pos. Get rid of the unsightly trunking. What do ya think?
 
There is no requirement in BS7671 for mechanical protection to be earthed.
So not a sweeping generalisation, a simple statement of fact.
 
Last edited by a moderator:
I'd be dubious about running it using a supposed safe zone from a room thermostat that itself has got surface mounted cable. The room stat is something that's likely to get moved / replaced at some stage, and anyone would assume that the only cable run to it / likely to be in that safe zone would be the one that's surface mounted.

technically it's arguable, but going with the spirit of the regs, it wouldn't seem a wise move to me.
 
There is no requirement in BS7671 for mechanical protection to be earthed.
So not a sweeping generalisation, a simple statement of fact.

Steel conduit and trunking are mechanical protection and require earthing
Any mechanical protection which is an extraneous part needs to be bonded
 
Last edited by a moderator:
Steel conduit and trunking are mechanical protection and require earthing
And mechanical protection which is an extraneous part needs to be bonded

how's it an extraneous conductive part if it's buried in the wall?

mechanical protection and earthed metal capping are 2 separate protective measures, it doesn't need to be earthed as long as it actually does provide protection against nail penetration.
 
how's it an extraneous conductive part if it's buried in the wall?

mechanical protection and earthed metal capping are 2 separate protective measures, it doesn't need to be earthed as long as it actually does provide protection against nail penetration.

He made a blanket statement about mechanical protection, nothing specific about it being buried in anything
 
It doesn't matter whether it's buried or not, there is no requirement in BS7671 for mechanical protection to be earthed.
You want to earth it carry on, I'll get you some PVC conduit to earth.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Mechanical protection/ Safe zones
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
sparrrrk,
Last reply from
Deleted member 26818,
Replies
28
Views
4,520

Advert

Back
Top