Do you carry out an insulation resistance test on a 3 phase motor with thermistor protection as you would without thermistor protection or does extra caution or process need carrying out differently?
First time coming across one
agree with @westward10 ,
if the thermistor terminals are separate to the windings ( I expect they are) then it is also worth testing resistance between thermistor and each winding (should be open circuit, any connection between thermistor and winding is normally a sign of a melted motor.