Discuss Memera 2000 RCD Question (A100HE) in the UK Electrical Forum area at ElectriciansForums.net
1strangefish
Hi Guys,
Have seen some similar threads on these boards but still after some wisdom . . .
At clients yesterday and completed tests on a lighting circuit that was moved to the RCD side of the board.
Came to complete the RCD tests before packing up to go home and that is where it all began!
Using a Meggar MFT 1553 on auto set at 30ma
Got the following results:
x1/2: no trip
x1 (0): 69 ms
x1 (180): 113ms
x5 (0): 40ms
x5(180) 41.3ms
Retested (on Auto test) a further 4 times and had pretty much the same results except at for the x5 (180) where it then failed to trip, always reaching 1999 ms.
I need to go back and test just the RCD with the rest of the system isolated, but have never come across a fault like this before. Any/all help and advice greatly appreciated.
Fish
Mem rcds frequently give sh@@ readings in my experience, you can replace them as you can get them easy enough, but I'd check the little earth wire is connected properly and you have adequate Ze readings
Hi,
Having tested that particular type of RCD in the past I can confirm those readings are about right for that type of RCD. Not saying they are acceptable but they always in my experience have higher test readings than other comparable units.
Regards.
Hi Guys,
x1/2: no trip
x1 (0): 69 ms
x1 (180): 113ms
x5 (0): 40ms
x5(180) 41.3ms
Fish
When you come to testing RCD directly at the RCD terminals with the final circuit isolated, be aware of MEM technical support advice that the protective device should have a minimum 'load' of 1m T&E cable connected to it otherwise misleading results are possible.
Reply to Memera 2000 RCD Question (A100HE) in the UK Electrical Forum area at ElectriciansForums.net
Morning everyone, this is my first post - although i had an account years before that seems to have been lost. Can any of you shed some light...
5K
Afternoon all, As we all know the new 18th certs only have the facility to record the x1 trip time of a circuits RCD in the test results page...
28K
Deleted member 26818
Tested an RCD spur earlier with some odd results Tested at x 1/2 (both waveforms) and no trip x 1 (0 degrees = 28.5 ms), (180...
4K
E
doing an EICR today i could not take Zs readings at any sockets on various circuits protected by a RCD tester set to low , no trip test and trips...
On completion of some recent minor work , I carried out the usual testing and noticed the incoming 100A 30mA rcd on the Consumer unit was failing...
4K