Small commercial install,it's actually a community centre.

Anyway,the main metered DB containing all the sub-main distribution circuits (just five I think) is plastic.So we have the main tails into this DB,then each sub main is seperately metered into what will be become the room containing the new meters.

The spec for the sub mains states that each feed is to be wired in SWA,all DB's will be plastic.So I've got to feed five meters (plant room,power,lighting,o/s lighting) and then join my SWA from the meters.

How is this the best way to do this,how would you do it? I've already queried the plastic db's and got a 'use what you've been given' type response.So i suppose really what I'm saying is,the best way to connect tails to SWA is?

:D
 
ive done this before by mounting an adaptable box, glanding the armoured in to that then using henley block connectors to join on to the meter tails.
 
Hi.

Agree with DHES. Also Newlec style adaptable boxes come fitted with a din rail type mounting bar and their own large mountable connectors that sit neatly inside the enclosure.
 
OK thanks for the quick replies.

I was thinking adaptable boxes but wasn't sure how to actually make the connection.Both your methods sound fine to me.

Cheers and duly thanked.
 
I would use the adaptable box mounted against the sub board, for the SWA termination and then take the cores through the other side of the box into the sub board, straight into the terminals.

Saves having to mess about with jointing.

Or am i missing the point?:D
 
Last edited by a moderator:
I would use the adaptable box mounted against the sub board, for the SWA termination and then take the cores through the other side of the box into the sub board, straight into the terminals.

Saves having to mess about with jointing.

Or am i missing the point?:D

I need to come out the sub board though Jason into seperate meters for each distribution circuit,so somewhere along the line I need to joint tails onto SWA.

(Unless it's me not getting what you're saying :D)
 
I've done this before as well.SWA glanded onto a 4x4 adaptable box into a henley block and connect tails into henley block and then to board:p
 

Reply to Meter tails to SWA in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock