Hi. I've recently moved into new house. The meter box and consumer unit are installed in cupboard underneath the stairs, however they are approx. 1.5m apart and the tails are surface mounted. Should they be encased in trunking so as to protect them from damage. Thanks
 
Hi. I've recently moved into new house. The meter box and consumer unit are installed in cupboard underneath the stairs, however they are approx. 1.5m apart and the tails are surface mounted. Should they be encased in trunking so as to protect them from damage. Thanks
No they don't have to be encased in trunking but should be adequately supported. Is this a new build with consumer unit under the stairs?
 
The tails are insulated and sheathed and are considered adequate for the use you describe as long as they are supported adequately
Plastic trunking would not provide much in the way of mechanical protection
 
Can't think it would be a new build house, with the CU in a cupboard under stairs, unless the stairs were the Ewing Mansion of Southfork!
It would be a rubbish design if it was a new build and positioned under the stairs.
 
Don't think it's a bad idea, for tails in trunking, especially under stairs. Stops em being used as coat hooks and the like.
 
Many are done like this, but it doesn't make it attractive. The back wall equipment could be "put in a cupboard" perhaps, which at least will stop all your kit being thrown at it.
 