Discuss MFT shows 235V, Drummond tester says dead, no live present in the UK Electrical Forum area at ElectriciansForums.net

T

The Ghost

Attended call out at shop. Freezers, chillers and tills were down. Using MFT on V. measurement got 235V plugged into socket. Tested inside socket at terminals with drummond tester, nothing 0 V. Switched MFT to Loop and the neutral was missing. Just a bit puzzled why the MFT shows V. and Drummond 0 V. The neutrals in the neutral block had cooked away, loose neutrals and so on. I would post a pic but the forum does not allow me to post any pics any more.
 
It's easy to get caught out. Some time back I tested a socket at the terminals with an older 2 probe voltage tester both L-N and L-E. Dead. Disconnected socket and promptly got a handful off the live. Turned out the N had gone missing and the earth had never been connected.
The moral being always follow safe isolation procedure and use an approved 2 probe voltage tester which indicates voltage even if only one conductor is present.
 
Never assume! Check the instructions for your particular MFT as the voltage measurement strategy varies between models. E.g. I think the Megger 1500 displays the L-E voltage by default, while the 1700 series displays the highest voltage present between any pair of leads if all are connected. So could display L-E or L-N, or even N-E if L is missing.
 
Some times my MFT, when set to test Zs , will show no volts, yet I know there there is power there.
I switch the MFT off then on again, re-test and then it reads the voltage. I wouldn’t be trusting a MFT to verify if a circuit is live or dead.
 
Just so you know guys...I would not even stick your hands where they shouldn't be without using a BS61010 BS EN 61243-3 GS38 approved two pole voltage tester so please try not to worry about me using the wrong equipment for the job but thanks for your concern in any event. I was merely highlighting the caution regards why not to use MFT (Which we all know we should not) I think as @buzzlightyear said the voltage indicator is not needed as it is may be dangerous not just undesirable.
 
The voltage indicator setting is sometimes useful for say measuring voltage present at various points for volt drop etc
 
Looking at my Kewtech 65DL to test for voltage you must use the L and PE terminal for the leads, not the neutral. But what was useful using the three lead plug top lead, is it showed the missing neutral. So I knew where to look for the problem or took a well educated guess I should say.
 
interesting...... soon as i've had my breakfast smoke to kick-start the old lungs, going to have to connect 1553 to a socket with the N dissed.see what it says. no animals will be hurt during the course of the experiment.
 
an approved 2 probe voltage tester which indicates voltage even if only one conductor is present.
This is wrong and a dangerous misunderstanding.
If only one conductor is present then by definition there is no voltage present. The only tester that only needs one pole is a volt stick and we all know about them.
You can test between all conductors in an accessory as no volts and still have a dangerous voltage present. This would be especially likely in a light switch without earth and looped at the rose.
If you want to test you really need to test against all terminals and all exposed metallic items in t vicinity. Imagine touching an earthed radiator at the same time as a live light switch.
 
This is wrong and a dangerous misunderstanding.
If only one conductor is present then by definition there is no voltage present. The only tester that only needs one pole is a volt stick and we all know about them.
You can test between all conductors in an accessory as no volts and still have a dangerous voltage present. This would be especially likely in a light switch without earth and looped at the rose.
If you want to test you really need to test against all terminals and all exposed metallic items in t vicinity. Imagine touching an earthed radiator at the same time as a live light switch.
suppose that beats the wet finger.
 

Reply to MFT shows 235V, Drummond tester says dead, no live present in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K
G
I'm trying to get my head around inspection and testing. When I'm struggling, i often find writing it down helps me to learn it - please could you...
Replies
7
Views
1K
F
Here is the second half of the long answer questions. Q 24 a) Describe how an Insulation Resistance test would be carried out on the new lighting...
Replies
5
Views
9K
Deleted member 26818
D
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K
T
This week, I finally decided to get on with rejuvenating the supply to my garage. This was in place when we moved in and, in all honesty (and on...
Replies
11
Views
2K
Engineer54
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock