Attended call out at shop. Freezers, chillers and tills were down. Using MFT on V. measurement got 235V plugged into socket. Tested inside socket at terminals with drummond tester, nothing 0 V. Switched MFT to Loop and the neutral was missing. Just a bit puzzled why the MFT shows V. and Drummond 0 V. The neutrals in the neutral block had cooked away, loose neutrals and so on. I would post a pic but the forum does not allow me to post any pics any more.
Yes @Strima seems to be the obvious conclusion but one would normally expect it to ref. Neutral so a small caution re using MFT for V. Testing. I will check with the manufacturer regards this interesting finding.
It's easy to get caught out. Some time back I tested a socket at the terminals with an older 2 probe voltage tester both L-N and L-E. Dead. Disconnected socket and promptly got a handful off the live. Turned out the N had gone missing and the earth had never been connected.
The moral being always follow safe isolation procedure and use an approved 2 probe voltage tester which indicates voltage even if only one conductor is present.
Never assume! Check the instructions for your particular MFT as the voltage measurement strategy varies between models. E.g. I think the Megger 1500 displays the L-E voltage by default, while the 1700 series displays the highest voltage present between any pair of leads if all are connected. So could display L-E or L-N, or even N-E if L is missing.
Some times my MFT, when set to test Zs , will show no volts, yet I know there there is power there.
I switch the MFT off then on again, re-test and then it reads the voltage. I wouldn’t be trusting a MFT to verify if a circuit is live or dead.
Just so you know guys...I would not even stick your hands where they shouldn't be without using a BS61010 BS EN 61243-3 GS38 approved two pole voltage tester so please try not to worry about me using the wrong equipment for the job but thanks for your concern in any event. I was merely highlighting the caution regards why not to use MFT (Which we all know we should not) I think as @buzzlightyear said the voltage indicator is not needed as it is may be dangerous not just undesirable.
Looking at my Kewtech 65DL to test for voltage you must use the L and PE terminal for the leads, not the neutral. But what was useful using the three lead plug top lead, is it showed the missing neutral. So I knew where to look for the problem or took a well educated guess I should say.
@Vortigern if you want to query tech stuff with kewtech the man to ring is alan towler, hes the tech support guy, very helpful and normally has the answers. his info is on the kewtech site but save you having to go on to it, his number is 07970826188.
interesting...... soon as i've had my breakfast smoke to kick-start the old lungs, going to have to connect 1553 to a socket with the N dissed.see what it says. no animals will be hurt during the course of the experiment.
I did not use single leads I used the three lead one with the plug top on the end by the way. If you use two single leads you have to use L and PE on my MFT.
This is wrong and a dangerous misunderstanding.
If only one conductor is present then by definition there is no voltage present. The only tester that only needs one pole is a volt stick and we all know about them.
You can test between all conductors in an accessory as no volts and still have a dangerous voltage present. This would be especially likely in a light switch without earth and looped at the rose.
If you want to test you really need to test against all terminals and all exposed metallic items in t vicinity. Imagine touching an earthed radiator at the same time as a live light switch.
This is wrong and a dangerous misunderstanding.
If only one conductor is present then by definition there is no voltage present. The only tester that only needs one pole is a volt stick and we all know about them.
You can test between all conductors in an accessory as no volts and still have a dangerous voltage present. This would be especially likely in a light switch without earth and looped at the rose.
If you want to test you really need to test against all terminals and all exposed metallic items in t vicinity. Imagine touching an earthed radiator at the same time as a live light switch.
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical
forum online. General electrical questions and answers can be found in the electrical forum.
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.