Hi Guys,
I went to see a job the other day and even though its a new splitload C/U, it had about 3 breakers with more than one circuit wired in. ie ....

6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm

20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom.

32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer.

Now what would you do in my posistion regarding this situation as the location of the C/U is very tight and wouldnt stretch to a larger unit with more ways?

Finally the Shower was a 9.5 KW fed with 6mm clipped direct and only about a 6m length, this was protected by a 40A. I measured the Amp draw whilst it was on full power and lest it on for quite some time and it never got near 30Amps never mind 40...marginal cable but the sums seem to add up...should I change the cable???:confused:
Cheers...
 
Hi Guys,
I went to see a job the other day and even though its a new splitload C/U, it had about 3 breakers with more than one circuit wired in. ie ....

6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm No problem

20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom. Again,no problem

32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer. Would be preferable to split...but complies with regs

Now what would you do in my posistion regarding this situation as the location of the C/U is very tight and wouldnt stretch to a larger unit with more ways?

Finally the Shower was a 9.5 KW fed with 6mm clipped direct and only about a 6m length, this was protected by a 40A. I measured the Amp draw whilst it was on full power and lest it on for quite some time and it never got near 30Amps never mind 40...marginal cable but the sums seem to add up...should I change the cable???:confused:
Cheers...
A 9.5kw load should pull over 41a...exceeding the rating of the MCB but not the cable @ 47 amps clipped direct...at 6m volt drop is <2V.....as long as the mcb is not tripping during use I wouldnt worry about it.
 
in regards to the circuits mate, the 6a supply to the burglar alarm is allowed as its a spur off the circuit, as is the radial sockets. as for the shower, i make it 41A assuming 230v and a power factor of 1.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
More than one ciruit in a breaker?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
eyeball,
Last reply from
mcummins7,
Replies
7
Views
1,878

Advert

Back
Top