Discuss More than one ciruit in a breaker? in the Australia area at ElectriciansForums.net
E
eyeball
Hi Guys,
I went to see a job the other day and even though its a new splitload C/U, it had about 3 breakers with more than one circuit wired in. ie ....
6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm
20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom.
32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer.
Now what would you do in my posistion regarding this situation as the location of the C/U is very tight and wouldnt stretch to a larger unit with more ways?
Finally the Shower was a 9.5 KW fed with 6mm clipped direct and only about a 6m length, this was protected by a 40A. I measured the Amp draw whilst it was on full power and lest it on for quite some time and it never got near 30Amps never mind 40...marginal cable but the sums seem to add up...should I change the cable???:confused:
Cheers...
Hi Guys,
6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm No problem
20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom. Again,no problem
32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer. Would be preferable to split...but complies with regs
Cheers...
A 9.5kw load should pull over 41a...exceeding the rating of the MCB but not the cable @ 47 amps clipped direct...at 6m volt drop is <2V.....as long as the mcb is not tripping during use I wouldnt worry about it.
in regards to the circuits mate, the 6a supply to the burglar alarm is allowed as its a spur off the circuit, as is the radial sockets. as for the shower, i make it 41A assuming 230v and a power factor of 1.
Reply to More than one ciruit in a breaker? in the Australia area at ElectriciansForums.net
  • Locked
5K
Hi all, I’m new to this forum so please bear with me. I live in a bungalow and would like to repurpose an unused shower cable to supply one new...
4K
S
Hi, newbie here. Friend has asked for opinion on quote from another sparky. Single radial to conservatory replacement. Proposal is 6mm2 feed for 4...
Engineer54
E
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
77K
S
Here is a list i have just copied off my website Teague Electrical - Home M.C.B. (Miniature Circuit Breaker) Electronic version of a fuse...
8K
Plonker 3
P