Any of the energy suppliers can trace the MPAN if you quote them the whole meter ID number and the post code.

Also, do you actually need a 3ph system on a house build? It would be cheaper to get a whole new supply put in and probably a much cheaper 1ph would suffice.

Oh, and you probably won't satisfy your voltage drop requirements with that size of cable over that length, btw.


Will have a look for code on it.

Yes he needs 3 phase for machinery in garage.
 
I know it's money NOT going in your pocket, but you'll find the DNO's will charge less for a whole entire incomer move than you could even buy the cable for to extend it, plus have no worries about Vd and also probably get a better Ze out of the deal, too.
 