E

ezzzekiel

Been to a large house single phase (very posh) has 5 db scattered around the place all of which have rcd and are fed from mcb in first db which also has rcd, fault knokcked out a different rcd and scratching head as how to provide correct discrimination and providing 30ma rcd protection whilst dividing circuits any thoughts on matter.
 
Been to a large house single phase (very posh) has 5 db scattered around the place all of which have rcd and are fed from mcb in first db which also has rcd, fault knokcked out a different rcd and scratching head as how to provide correct discrimination and providing 30ma rcd protection whilst dividing circuits any thoughts on matter.

Can you change the RCD in DB1 to a time delay 'S' type if it needs to be there?

If the house is divided into 5 DB's then is division of circuits not already satisfied?
 
Assuming db1 everything had been switched off and couldn't get much sense. Db1 powers the other db plus about 5 circuits was rewired by part p reg about 3 years ago no paperwork.
Figured all rcbo or s type and rcbo for main db
 