Is this the correct way of wiring npn sensor 4 wire with solid state relay and solenoid valve?

Screenshot_20191011-155509.jpg
 
I can see a few problems there...

(EDITED)

1) The wiring to the sensor and relay is muddled up, you have the load side of the relay going back to the sensor instead of out to the valve (which I assume is connected to the terminal block externally.)
2) Which of the two SSR types shown are you using? The S102S11 has a triac output for AC loads only and cannot switch DC (it will stick on permanently). FWIW it also needs an external input current setting resistor. The SSR 10DD is DC output although there seem to be a variety of different versions of it.
3) Does the relay need a snubber / catch diode for the solenoid coil, or is that internally suppressed? Do you need a shunt resistor across the relay input to allow for sensor output leakage (what it its off-state current threshold?)
 
Last edited:
I can see a few problems there...

(EDITED)

1) The wiring to the sensor and relay is muddled up, you have the load side of the relay going back to the sensor instead of out to the valve (which I assume is connected to the terminal block externally.)
2) Which of the two SSR types shown are you using? The S102S11 has a triac output for AC loads only and cannot switch DC (it will stick on permanently). FWIW it also needs an external input current setting resistor. The SSR 10DD is DC output although there seem to be a variety of different versions of it.
3) Does the relay need a snubber / catch diode for the solenoid coil, or is that internally suppressed? Do you need a shunt resistor across the relay input to allow for sensor output leakage (what it its off-state current threshold?)

1) Yes there is a solenoid valve. Muddled up? Can u explain a more on that?
2) Sorry for the confusion. Im using the SSR 10DD
3) Internally suppressed. Doesnt need resistor.

Confuse of the wiring because its based on the previous drawing. i just modify it by using sensor.

Capture.PNG
 
Last edited:
You do need some new specs MW. The sensor is shown as having two 'out -' terminals, one of which is connected to the input of the relay and one to the output, while its +ve supply is shown coming from the -ve of the PSU via the solenoid. It's all jumbled. OP, please post the spec / link for the sensor so we know how that is actually connected inside.
 
You do need some new specs MW. The sensor is shown as having two 'out -' terminals, one of which is connected to the input of the relay and one to the output, while its +ve supply is shown coming from the -ve of the PSU via the solenoid. It's all jumbled. OP, please post the spec / link for the sensor so we know how that is actually connected inside.


Im using the
1)SSR 10DD for the relay

2)Baumer Diffuse Sensor with background suppression O300.GR . 4 wire
(https://www.baumer.com/ch/en/produc...1T_72CU_0000_web_EN.pdf?mediaPK=8800337133598)

3)100-240V AC, 8 terminal strip and solenoid valve.
[automerge]1570841386[/automerge]
TheNewguy the drawings looks right but my eyes are getting bad due to old age and I can’t read the writing

Im sorry its so small. Here the new drawing and wiring. If u you can verify it would be really helpful to me
Capture.PNG

[automerge]1570841488[/automerge]
You do need some new specs MW. The sensor is shown as having two 'out -' terminals, one of which is connected to the input of the relay and one to the output, while its +ve supply is shown coming from the -ve of the PSU via the solenoid. It's all jumbled. OP, please post the spec / link for the sensor so we know how that is actually connected inside.

Here the new wiring that i modify based on what u said on the previous reply
Capture.PNG
 
You do need some new specs MW. The sensor is shown as having two 'out -' terminals, one of which is connected to the input of the relay and one to the output, while its +ve supply is shown coming from the -ve of the PSU via the solenoid. It's all jumbled. OP, please post the spec / link for the sensor so we know how that is actually connected inside.

for the additional information. the sensor is push pull sensor.
 
the system use ssr 10dd, solenoid valve and baumer sensor push pull.
I’m sorry I can’t help you
[automerge]1570847229[/automerge]
the system use ssr 10dd, solenoid valve and baumer sensor push pull.
You are in electronics I’m in electrical I know hoe to wire a solenoid you have a solid state relay which needs power to energize then are your contacts N./O or N/C. I guess I need you to paint me a picture of how your devices work and 1 wire had 2 separate numbers on it
 
Last edited:
sorry sir. the contact is N/O. the sensor is use to detect with background suppresion. when it detect the solenoid valve open and push the air out. i hope it can clarify the imformation that u needed

Capture.PNG
[automerge]1570850181[/automerge]
You do need some new specs MW. The sensor is shown as having two 'out -' terminals, one of which is connected to the input of the relay and one to the output, while its +ve supply is shown coming from the -ve of the PSU via the solenoid. It's all jumbled. OP, please post the spec / link for the sensor so we know how that is actually connected inside.

Im using the
1)SSR 10DD for the relay

2)Baumer Diffuse Sensor with background suppression O300.GR . 4 wire (https://www.baumer.com/ch/en/produc...1T_72CU_0000_web_EN.pdf?mediaPK=8800337133598)

3)100-240V AC, 8 terminal strip and solenoid valve.
 

Attachments

  • Capture.PNG
    Capture.PNG
    36.6 KB · Views: 34
sorry sir. the contact is N/O. the sensor is use to detect with background suppresion. when it detect the solenoid valve open and push the air out. i hope it can clarify the imformation that u needed

View attachment 53074
[automerge]1570850181[/automerge]


Im using the
1)SSR 10DD for the relay

2)Baumer Diffuse Sensor with background suppression O300.GR . 4 wire (https://www.baumer.com/ch/en/produc...1T_72CU_0000_web_EN.pdf?mediaPK=8800337133598)

3)100-240V AC, 8 terminal strip and solenoid valve.
Is that terminal block inside the valve ?
sorry sir. the contact is N/O. the sensor is use to detect with background suppresion. when it detect the solenoid valve open and push the air out. i hope it can clarify the imformation that u needed

View attachment 53074
[automerge]1570850181[/automerge]


Im using the
1)SSR 10DD for the relay

2)Baumer Diffuse Sensor with background suppression O300.GR . 4 wire (https://www.baumer.com/ch/en/produc...1T_72CU_0000_web_EN.pdf?mediaPK=8800337133598)

3)100-240V AC, 8 terminal strip and solenoid valve.
all the valves I’ve worked on is air to open and spring to close
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
malaysia
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Malaysia
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Need Advise!! Help me with this wiring. NPN sensor/Solid State Relay
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
thenewguy,
Last reply from
Megawatt,
Replies
18
Views
3,214

Advert

Back
Top