Changing a CU without doing an eicr first is asking for trouble, and as stated it's proberbly the Immersion element
Discuss Neutral earth fault in the UK Electrical Forum area at ElectriciansForums.net
but must be labelled . ie fridge freezer
Next time i need to add some sockets to a bedroom I'm gonna use the immersion heater radial PMSL :freak:
L-N?...are you sure?...Yeah disconnect the element from the supply and try IR between L-N and N-E if eaither are short theb that's mostly your problem. You'll get dead shhort between L-N but you knew that anyway
L-N?...are you sure?...
Reply to Neutral earth fault in the UK Electrical Forum area at ElectriciansForums.net