Once we found and removed/ rectified the fault the RCD started functioning normally againHow did you fix the issue?
I agree, I just spoke to the spark he said he did a I.r. test and its fine.Once we found and removed/ rectified the fault the RCD started functioning normally again
Was over the required 38M it was. Ill go back change all cpc to the correct size. I read this could be the issue.What IR results did you get for each circuit?
I read that you can get a error from neutral to protective earth if the cpc is oversized.the extended cpc has nothing to do with it. you have a N-E fault on the ring circuit which is inhibiting thr RCD. i don't know the theory behind this but i've had it a couple of times.
OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?the extended cpc has nothing to do with it. you have a N-E fault on the ring circuit which is inhibiting thr RCD. i don't know the theory behind this but i've had it a couple of times.
Its not the "oversized" cpc. You've been told that. Have you measured earth leakage from the circuit whilst energised? Have you done an IR test of the circuit to the MET, have you ensured the neutrals are in the correct bar. Have you split the circuit in half and tried energising 1 leg?OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
No he's grabbed the money, ----ed off, saying he's busy.The spark you are working with should know what tests to do.
What's his opinion on you wanting to change the size of the CPC? Does he agree?
Now with the new board on were getting a neutral fault showing on socket ring.
In your OP, you say there is a neutral fault. Later you say the circuit has passed IR. Please can you explain this, so we are better placed to advise?OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
No I paid him. From my own pocket, the customer is going to pay me.He's been paid for the job despite it not being complete? And left his trainee to fix it? Why did the customer pay him before the job was finished?
Are we getting the full story here?
No I paid him.
Ye, I think so.I think your customer is going to have to get a qualified spark in to sort this out.