and why a 1.5mm for the extractor.....1.0mm more that sufficient here.....
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

4MM would probably do for the cooker, but 6MM is better in case of changes down the line, bigger hob fitted etc. With such a short run the cost of cable is going to be minimal anyway.
 
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

4MM would probably do for the cooker, but 6MM is better in case of changes down the line, bigger hob fitted etc. With such a short run the cost of cable is going to be minimal anyway.
well that sounds fair.....its just that i keep seeing 6mm mentioned in this forum.....when it just aint necessary.....it also says to me that there are some coming in here asking away.....who cant get their head around diversity and/or cable calcs......
 
Last edited by a moderator:
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

Besides 1.5mm cable is the minimum csa allowed for S/O's or FCU's.

see App 15/15B (BGB) the Note at the bottom right of the page.

reg 524.1 and table 52.3 (BGB)
 
Last edited by a moderator: