I think I was writing something else and it went in on the top of last reply. I was just trying to say that I made sure I was doing it safely while unscrewing the earth block.
Thanks. So it seems to me that the first electrician is the right person for the job. I was just reluctant that he quoted me without a site visit. May be the pictures were good enough to give him the idea about the state of wiring.any electrician can change that main earth conductor. as you say, main switches are usually 100A. both in isolator and CU.
He told me no need for water pipe bonding. The gas pipe he is going to bond with 10sqmm cable. I have informed him that the gas pipe outside is plastic but he is going to bond it anyway. May be he doesn't want to spend time to test and calculate and it is much easier just to bond.As you have mentioned there are requirements for the sizing of the main earthing conductor.
The bonding conductors also need to be sized correctly. As a default we used to bond all services (water/gas etc), but recently this requirement has changed and we now test to see if an earth potential is introduced through your service pipework.
If there's no earth potential then it doesn't require bonding. If there is a potential then we bond it.
This recent change is due to the increased usage of plastic service pipes.
I raised this issue with him and he said that MCBs should be fine as we already have plugin MCBs without any issues. If RCBOs start showing some faults as they are more sensitive then either we rectify the relevant wiring if feasible or he will take the RCBO out and fit the MCB. I am not satisfied with this response. What is the point of upgrading if a MCB/Fuse is going to replace a MCB without a RCD. We certainly won't be able to chase any new cables downstair because of tiles and laminate floor. Even the new circuit in the kitchen is going to run under the kitchen cabinets until the next kitchen refit.It's all very well quoting by sight on a new CU but when it comes to fitting and all the RCD are popping off becuase there are faults on the circuits on the new RCD are you ready to fork out on fault finding which is sometimes very expensive? This is why an EICR is offered first to identify faults before hand. If not then it's a bit of a shot in the dark and you may get into some expensive costs. Sometimes it is easier and cheaper to re-wire than look for faults which may or may not be able to be corrected. I should proceed with caution were I you.
You are right to not accept that response.I raised this issue with him and he said that MCBs should be fine as we already have plugin MCBs without any issues. If RCBOs start showing some faults as they are more sensitive then either we rectify the relevant wiring if feasible or he will take the RCBO out and fit the MCB. I am not satisfied with this response
Ok so it makes sense to do EICR. I got nearly five weeks and will take up my concerns with him.You are right to not accept that response.
MCBs only pick up on over-current, they do not care about potentially dangerous mistakes such as:
The above should be apparent on testing, and really that ought to be done before you start so you at least have a good idea of the possible cost to put everything right. While some won't do a full EICR first, most sane electricians would do a little inspection and some tests first just so they can eliminate some of the above.
- a N-E short
- swapped N &E at an outlet
- a "borrowed" neutral on up/down lighting circuits, or
- very poor/damaged insulation that is only a short journey from fire-starting.
If RCBOs start showing some faults as they are more sensitive then either we rectify the relevant wiring if feasible or he will take the RCBO out and fit the MCB.
I agree with you that SPD gives an additional protection, but I am not convinced yet for their use in a home as a standard device yet. There is no case record to warrant SPDs at this time. As you said most of the mains equipment can handle some surges and the most sensitive equipment as computers etc, people do use surge protectors anyway. At least I do. The current faults can occur but I never experienced one . There could be scenarios, where SPDs are better suited.I'm not sure what you have read about the SPD, but they rarely cause trouble and these days most CU come with one as standard. Cost is modest, typically a few tens of pounds now, and compared to the whole CU change (or analysing risk for fitting or not) not worth omitting.
It is not always lightning spikes that can be a risk, it can be high current faults being disconnected.
For most of the time you ought not to need them as mains equipment is supposed to stand a few kV impulse voltage, but I would not put it past insurance companies to start weaselling out of claims if no SPD!
You are right, it does create doubt in mind that's why I said that I am not satisfied by his response.The idea that the solution to faults with RCBO be dealt with by replacing with MCBs is very poor to dangerous thinking/practice. Did he arrive on a horse by any chance?