Haven't you seen the pic? It's an ancient rewireable Wylex, with a fuse cover that's missing/unfittable. On the plus side, it isn't plastic.Why are you changing the CU anyway?
Discuss New CU and meter tails etc in the UK Electrical Forum area at ElectriciansForums.net
Haven't you seen the pic? It's an ancient rewireable Wylex, with a fuse cover that's missing/unfittable. On the plus side, it isn't plastic.Why are you changing the CU anyway?
I have asked him if he can provide me a quote either with a wylex cu or deduct the amount of cu and rcbos and I will supply him direct. I have given him the links of TLC for this, not sure if he shops at TLC. I have a TLC store about 2 miles from my home and can pick up the stuff in about 20 minutes.It seems as though the first electrician meets your requirements, other than the fact that you've expressed a preference for having a different brand of CU fitted. Why not just ask him for an ammended quote to account for this?
Thanks. So it seems to me that the first electrician is the right person for the job. I was just reluctant that he quoted me without a site visit. May be the pictures were good enough to give him the idea about the state of wiring.any electrician can change that main earth conductor. as you say, main switches are usually 100A. both in isolator and CU.
He told me no need for water pipe bonding. The gas pipe he is going to bond with 10sqmm cable. I have informed him that the gas pipe outside is plastic but he is going to bond it anyway. May be he doesn't want to spend time to test and calculate and it is much easier just to bond.As you have mentioned there are requirements for the sizing of the main earthing conductor.
The bonding conductors also need to be sized correctly. As a default we used to bond all services (water/gas etc), but recently this requirement has changed and we now test to see if an earth potential is introduced through your service pipework.
If there's no earth potential then it doesn't require bonding. If there is a potential then we bond it.
This recent change is due to the increased usage of plastic service pipes.
I raised this issue with him and he said that MCBs should be fine as we already have plugin MCBs without any issues. If RCBOs start showing some faults as they are more sensitive then either we rectify the relevant wiring if feasible or he will take the RCBO out and fit the MCB. I am not satisfied with this response. What is the point of upgrading if a MCB/Fuse is going to replace a MCB without a RCD. We certainly won't be able to chase any new cables downstair because of tiles and laminate floor. Even the new circuit in the kitchen is going to run under the kitchen cabinets until the next kitchen refit.It's all very well quoting by sight on a new CU but when it comes to fitting and all the RCD are popping off becuase there are faults on the circuits on the new RCD are you ready to fork out on fault finding which is sometimes very expensive? This is why an EICR is offered first to identify faults before hand. If not then it's a bit of a shot in the dark and you may get into some expensive costs. Sometimes it is easier and cheaper to re-wire than look for faults which may or may not be able to be corrected. I should proceed with caution were I you.
You are right to not accept that response.I raised this issue with him and he said that MCBs should be fine as we already have plugin MCBs without any issues. If RCBOs start showing some faults as they are more sensitive then either we rectify the relevant wiring if feasible or he will take the RCBO out and fit the MCB. I am not satisfied with this response
Ok so it makes sense to do EICR. I got nearly five weeks and will take up my concerns with him.You are right to not accept that response.
MCBs only pick up on over-current, they do not care about potentially dangerous mistakes such as:
The above should be apparent on testing, and really that ought to be done before you start so you at least have a good idea of the possible cost to put everything right. While some won't do a full EICR first, most sane electricians would do a little inspection and some tests first just so they can eliminate some of the above.
- a N-E short
- swapped N &E at an outlet
- a "borrowed" neutral on up/down lighting circuits, or
- very poor/damaged insulation that is only a short journey from fire-starting.