Hi guys,
A fairly basic question here, or rather clarification. I need to put in a temporary supply for the work men on site in my new build. There has been no power at the site before and NIE have just installed their transformer and pulled in their supply cable (100A TN-C-S supply). For connection of a temporary supply am I right in saying I need a 100A DP mains switch and earth iscoe for NIE to connect into out of their cut-out, a 30mA rcd and 16A mcb in a separate board feeding into a 16A 3 pin socket all enclosed in a standard pirelli box? Just to let you know I'm 16th edition and haven't upgraded yet hence the need for clarification.
thanks for any comments etc.
Jonny
A fairly basic question here, or rather clarification. I need to put in a temporary supply for the work men on site in my new build. There has been no power at the site before and NIE have just installed their transformer and pulled in their supply cable (100A TN-C-S supply). For connection of a temporary supply am I right in saying I need a 100A DP mains switch and earth iscoe for NIE to connect into out of their cut-out, a 30mA rcd and 16A mcb in a separate board feeding into a 16A 3 pin socket all enclosed in a standard pirelli box? Just to let you know I'm 16th edition and haven't upgraded yet hence the need for clarification.
thanks for any comments etc.
Jonny