hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
 
if that reading is 120Meg. then it's fine. worry not. now link out L-E at 1 end and measure R1+R2. do the same with N-E. the 48 volts could be due to a broken or poor connection on the cpc.
 
m or M??????? need to get it right. one is milli ohms, the other is Meg ohms.
 
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
listen kid...
after reading this..jack it in...go get an experienced electrician in as Mr Biff has said...
 
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
120meg ohm?? If so then its fine your allowed 2 ... It's just people have a tendency to write +200meg ohm on the test sheet and people get led to believe that's the minimum.. I'd happily put my tongue on the insulation with that much resistance mate :)
 
experience comes with experience.long time ago, i was wet behind the ears. then i got out of the bath.
 
quote_icon.png
Originally Posted by telectrix
experience comes with experience.long time ago, i was wet behind the ears. then i got out of the bath.



and was this the moment that you realised you had forgotten to bond the pipes...lol..

and was this the moment that you realised you had forgotten to bond the pipes...lol..


Not quite,this was the moment he realised the brown stuff should be deposited in the toilet
 
quote_icon.png
Originally Posted by telectrix
experience comes with experience.long time ago, i was wet behind the ears. then i got out of the bath.



and was this the moment that you realised you had forgotten to bond the pipes...lol..






Not quite,this was the moment he realised the brown stuff should be deposited in the toilet

Where is the "yuk" button??
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
uk

Thread Information

Title
new lighting circuit problems
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
baazab,
Last reply from
Octopus,
Replies
25
Views
2,907

Advert

Back
Top