Hello, I am a customer, not a trained electrician! My adult son is overseeing some electrical work on the house. He got an electrician out who suggested upgrading the board (which was decades old) and doing an EICR.

During initial discovery, the electrician found the meter's "tails" are too thin for the 100A meter fuse from the supplier. My son did ask if we could just get the supplier to downgrade the meter fuse but the electrician said they would probably refuse.

So the electrician fitted these new "tails" from the meter to the fuse box. But the cables aren't in the wall - they are in plastic trunking that enters the house underneath our downstairs toilet.

Is this safe? Surely this is before any RCD protection from the new fuse box? It's only a few centimetres from the toilet cistern and pipework running to outside tap. Pics attached.
 

Attachments

  • IMG_6672_a.jpg
    IMG_6672_a.jpg
    1.1 MB · Views: 94
  • IMG_6673_a.jpg
    IMG_6673_a.jpg
    1.1 MB · Views: 69
  • IMG_6671_a.jpg
    IMG_6671_a.jpg
    1.2 MB · Views: 85
Is this safe?

Yes, nothing wrong with it other than being a bit ugly.

Its generally safer for the tails to not be buried in a wall as being in an easily identifiable location means it's much easier to avoid having any accidents when doing any work in the area.

Generally the water is going to stay inside the pipes and cistern and not bother the tails, and even if there is a leak the tails would need to be fully submerged for quite a long time before the insulation degrades (probably in the order or months or even years)
 