I

iainco

Hello there

I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of warranty!

None of the wiring set up has changed other than a new AC plug for the Solis inverter. I have a 16-panel 4kw system.

It seems, when the inverter 'wakes' in the morning it trips the main house electrics RCD/consumer unit. The solar system is running through a 20amp RCD on the consumer unit and as I say, this is how it was originally installed (and worked well until the Sungrow failure!). I have replaced the RCD just in case that was the issue but it still trips at start-up.

Any suggestions please?

One thing I'm not clear on (install instructions vague?) is: should I run a separate EARTH cable from the AC side isolator switch to the Solis inverter's case? Could not having this be causing the daily trip?

Thanks
 
Can you post up a pic of your CU?

Is the solar on a shared RCD board. What is actually tripping? Main RCD?

Thanks

Norton
 
Can you post up a pic of your CU?

Is the solar on a shared RCD board. What is actually tripping? Main RCD?

Thanks

Norton
Hi Norton, the middle RCD/main protected circuits keeps tripping at start-up. Hope that helps? Thanks.
 

Attachments

  • IMG_0932.JPG
    IMG_0932.JPG
    429.7 KB · Views: 113
Can you post up a pic of your CU?

Is the solar on a shared RCD board. What is actually tripping? Main RCD?

Thanks

Norton
...the solar has been wired into a spare within the protected circuits area so ends up tripping the house sockets, cooker, shower etc that are on the protected RCD?
 
Dangerous as well. If an earth fault occurred, such as you making contact with live mains, the RCD should disconnect the power in a sufficiently short time to prevent you from being electrocuted. The RCD will switch off as intended, but power will still be being supplied by the PV array, until it detects the loss of mains power and shuts down as well. This time will be far greater than the time it takes to electrocute you.
 
Dangerous as well. If an earth fault occurred, such as you making contact with live mains, the RCD should disconnect the power in a sufficiently short time to prevent you from being electrocuted. The RCD will switch off as intended, but power will still be being supplied by the PV array, until it detects the loss of mains power and shuts down as well. This time will be far greater than the time it takes to electrocute you.
Just wondering if we ever got to the bottom of this?
Could this be the result of power on tests the Solis is doing?
 
Hello there

I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of warranty!

None of the wiring set up has changed other than a new AC plug for the Solis inverter. I have a 16-panel 4kw system.

It seems, when the inverter 'wakes' in the morning it trips the main house electrics RCD/consumer unit. The solar system is running through a 20amp RCD on the consumer unit and as I say, this is how it was originally installed (and worked well until the Sungrow failure!). I have replaced the RCD just in case that was the issue but it still trips at start-up.

Any suggestions please?

One thing I'm not clear on (install instructions vague?) is: should I run a separate EARTH cable from the AC side isolator switch to the Solis inverter's case? Could not having this be causing the daily trip?

Thanks
This is a known issue with the S6 series. The inverter has internal Y-capacitors that produce a small leakage current to earth, enough to nudge a sensitive RCD toward tripping, particularly on startup when it's running grid connection checks.


First thing to check is what type of RCD is protecting that circuit. Type A can be sensitive to the pulsed DC leakage the Solis produces. Swapping to a Type A+ or Type F often sorts it without touching anything else.


Also worth checking the PV input earth setting in the inverter parameters. The S6 lets you select earthed or unearthed PV input, and if the previous Sungrow was configured differently there can be a mismatch with the existing install.


If it's only tripping at startup it's almost certainly the self-test routine. If it's tripping mid-generation that's a different issue worth looking at more carefully.
 