Talked to the tech line the other day hoping to confirm what I already knew, but with a definite answer regarding issues on EICR, on a property 40+ years old.
Not a great experience I must say, putting all the onus back on me, What do you think you should do?
At the end I gave a very conservative answer on the issues, saying well I wouldn’t be doing this NOW would I?
 
Last edited:
Guidance Note 8 talks about bonding in multiple occupancy dwellings and from memory is clear each flat should have extraneous services bonded to the MET in that flat at the point they enter that flat.
The question is more about the 6 sq mm CPC of the distribution circuit supporting the bonding I think.
 
Yea the problem is the CPC to the flats…that require MBPC..
The Meter positions are remote & are individual to each flat & so are the Water supplies to each flat & are extraneous parts.
No easy install for a new Earth Conductor & doubt if the LL would pay for it to be done
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Niceic technical help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
cliffed,
Replies
7
Views
1,103

Advert

Back
Top