That was my thinking too. And isn't the disconnection time for such sockets 5 seconds rather than 0.4 seconds? Does not answer the original question, but probably has some relevance.
It's all to do with reg 411.3.x which is about as clear as mud. It's one of those regulations that gives specific guidance for a particular application (sockets less than 32A) without being clear about how to go about installing anything other than that. Suggest you try posing your query in the IET forums - you may get a full answer from the bods on there (or you may not )
411.3.3
In AC systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket outlets with a rated current not exceeding 20A ......
(ii) mobile equipment with a current rating not exceeding 32A for use outdoors
though quite what kind of mobile equipment exists that is rated at over 32A is beyond me