What earthing system should be used on an off grid install with a solar inverter, wind inverter, battery backup inverter and a 4.5kW floating earth generator?
 

Richard Burns

-
Mentor
Esteemed
Arms
Reaction score
5,935
It depends on what the installation is powering.
With a floating earth generator it is hard to arrange a complete installation with anything other than a floating earth, however this is not safe if the installation is extensive.
 

Wilko

-
Esteemed
Arms
Reaction score
6,532
With a floating earth generator it is hard to arrange a complete installation with anything other than a floating earth ...

Hi RB - sorry in advance to ask dumb question - can the floating earth gen be reference to earth by externally connecting one of the floating outputs to gen body and earth stake?
 

Richard Burns

-
Mentor
Esteemed
Arms
Reaction score
5,935
You need a solidly earthed point connected to all the supplies that can be used as a permanent earth reference.
You should be looking to get a low resistance earth probably by using wide and deep earthing at multiple points.
The generator would need to be assessed to ensure that it can be solidly referenced to earth on one pole, (yes Wilko it should be possible but the design of the generator must be safe for this to do) it would be best to get an internally earthed generator designed for the purpose.
 
OP
B

bill01803

-
Esteemed
Arms
Reaction score
314
Leaving the generator out of it as it is plugged in and so can be disconnected, the supplies from the inverters don't appear have a reference to earth, I am waiting for a copy of the original cert to see what the installer claimed it to be.
As they are standard inverters presumably on a mains connected system it would rely on the dno for the earth reference, since this has been disconnected there doesn't appear to be one.
 
Reaction score
1,130
The inverts are both Aurora Uno
are you sure this is off grid, and not a hybrid system with grid connect and battery back up?

AFAIK those inverters don't have off grid functionality - or is the generator and demand big enough that they're able to take their reference from the generator and just reduce the demand from the generator?
 

Reply to Off grid earthing system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi installing my first solar PV on my own home before starting the courses next year and need some advice on earthing PV. System 6kw solar PV - 2...
Replies
13
Views
2K
Hi All, Main issue is as per title: inverter is stuck in Off-Grid mode. I used Self Use over the summer, which worked well, priority PV order...
Replies
7
Views
1K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
4K
Hi I would like to install an 8kw inverter with a battery in parallel with a 3kw inverter with a battery and about 1kw of solar I have 3kw solar...
Replies
0
Views
188
Hello all, To avoid too techy questions, i am the consumer not he installer. I have raised the issue with my installer who is researching it...
Replies
3
Views
541

New Posts (Please Reply)

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top