guys im replacing an electric shower like for like, the old shower was 9.5 kw, but was only on a 32 a mem type 1 321 qeb mcb, i told cliant it should be protected by a 40 amp breaker, trouble is the board is oldish and i dont know what breaker to fit,,,, also no rcd protection on boaed, are there any mem rcbo that will fit that board,tanx
 
it will be better for a mains replacment mate by the time you find a rcbo if ya lucky
i would replace just for my own peice of mind to be fair mate
 
if you leave the 32 amp, thats more safety than a 40 amp, unless thay have the shower on full heat, its not going to use all the amps anyway !
 
jason smith so u saying that i tell the lady o its safe as long as you dont use it on full power, saveloy its 6mm so can carry 56a if clipped direct so ok
 
M8 memshield 2 breakers fit them you can still get them RCBOs will cost you around 50 for the eaton breaker and the rcbo unit which attaches to the top :D
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
old mem consumer unit, help plezzzzzz
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
46
Unsolved
--

Advert

Thread statistics

Created
m25maintenance,
Last reply from
R.Sparky,
Replies
46
Views
19,776

Advert

Back
Top