H
highspark
Went to small job today. Fitting cooker to existing cooker point.
Before any connection
Done zs on circuit - tripped RCD.
Done rcd test no trip at 1x no trip at 5 x. This was on socket circuit aswell as cooker circuit.
Done ramp test. Ramped out at 33mA
Said cant install it. Circuit has failed.
Spoke to landlord. He said he'll send one of his sparks out. Got a phone call from other spark - nothing wrong with it.
Went back round to show him readings. He had dis board cover off and cooker socket case.Done exact same tests and everything was ok??????
What the hell went on there??
My meter is 6months inside calibration and was getting correct readings second time round. No trip on Zs all in tolerance on RCD tests.
Whats do you make of it?
Exactly the same place as second time round. On cooker circuit socket outlet.
Kitchen socket circuit.
Down Socket circuit.
Alll no trip on first visit.
Ah, I missed that you retested.
Hell knows, wonder if spark 2 had done something with the ccts he didn't tell you about?
edit...
Should really test at the device itself with all loads off.
Honestly cant put my finger on it. Other lad must have done something. He seemed go be a good enough spark. Vv strange
Good point ses, I've seen that, get much quicker readings after you trip them a couple of times.
I would replace the batteries and let the next calibration man aware, my tester sometimes plays up.
do think the landlord thinks you're trying to stitch him up
Landlord possibly does think that. But as I said to him get a third party in to test it. That way you will know.
As title says we're only as good as our machines.
Probably to do with a load which may of been on when testing first time around. Noise, leakage current all effect the operation of your meter.
Could be cold meter syndrome as I call it. Always used to get dodgy readings first thing in the morning (especially this time of year) when the meter was cold from being left in the boot all night. Remedy is to let it travel with you in the passenger footwell till you get to first job.
Only as good as our meters
Thread Tags
Tags Tags
meters
highspark,
Engineer54,