A block of flats has various external lights not just attached to the building but around the grounds. Part of the circuit has twin and earth going underground with good readings but clearly unsuitable cable for external/underground use (not contained in any form of conduit).
The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),
There are other ground lights that also have 2 core swa and the steel wire is not earthed (zero reading).
There is also no RCD protection for any external lights.
I am swaying between C1 and C2, so opinions appreciated.
Page 165 Blue OSG give a fairy comprehensive guide to EICR codes read and inwardly digest.
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.
I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.
I will look up reg when get a chance.
I was also under the impression from the draft that only dwellings would require RCD protection for lighting circuits regardless of installation method.
Not yet got my book though so can't check.
You are carrying out EICRs to the 18th Ed?
Very worrying.
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd
To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
B*gg*r! Yep your correct.
Pleased I haven't sent the EICR yet.
Also really pleased I'm part of forum. Could of been a changer there.
I don't like giving false information to clients, not good for my reputation.
Feel a bit embarrassed now. Why did I think this!
Another stupid regulation.
Why not in commercial premises?