i have been looking at regs for past two days only to confuse myself.pls somone help me .
what are res for outside lights at the moment.
regards aftab
 
regs for outside lights are whatever reg. in the brb is relevant.
 
Follow manufactures instructions, rcd protection if aint mounted to building fabric and cables arent suitably mechanicly prtected.... Sure there will be more and im sure i could be slightly wrong.....and will be corrected, so hang fire and dont go install them yet.. Hello!
 
Section 559 is directly related to lighting installations, but they are also covered all over the regs as is every installation.
 
Follow manufactures instructions, rcd protection if aint mounted to building fabric and cables arent suitably mechanicly prtected.... Sure there will be more and im sure i could be slightly wrong.....and will be corrected, so hang fire and dont go install them yet.. Hello!

Your more than slightly wrong old mate
 
Well as im doint 17th edition at moment, i do know there is loads of regs scattered that could relatre to the fitting of lighting outside, but lets be realistic here i mentioned most considertions.....
 
rcd protection if aint mounted to building fabric

Not sure where that regulation is from though
 
Telectrix back me up cause i got that one from one of your posts.... Many times am i going too need to read the regs book to be fluent in what im saying)
 
If the lights are 'outside' as you say, they are 'outside' the premises equipotential zone whether they are mounted on the outside wall or on a pole or other structure outside the building. So without question you require an RCD. Personally. I would install a separate circuit with a 30mA RCBO at the CU/DB.
 
If it's outside the equipotential zone, which these will be then it does need rcd protection because working on them or changing a lamp will mean the operative working from outside the equipotential zone, i.e. working from contact with the general mass of earth and therefore not protected by any earthing and bonding within the installation. 'AND' I know, Safe Isolation etc - doesn't matter there's no regulation which says if you safely isolate, you don't need rcd protection.
 
Last edited by a moderator:
There is NO requirement in BS7671:2008 to provide RCD protection to external lighting, where do these myths come from, does nobody read the BRB anymore?
 
If it's outside the equipotential zone, which these will be then it does need rcd protection because working on them or changing a lamp will mean the operative working from outside the equipotential zone, i.e. working from contact with the general mass of earth and therefore not protected by any earthing and bonding within the installation. 'AND' I know, Safe Isolation etc - doesn't matter there's no regulation which says if you safely isolate, you don't need rcd protection.

Davie as I tried to get the other lads to do have a read of section 559 with regard to RCD protection for lighting then 559.10.3.2. Yuo will see what the regs recommend
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Outside Lights Regulations
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
aftabjaved,
Last reply from
the pict,
Replies
48
Views
27,127

Advert

Back
Top