Is this circuit been calculated. Plus new circuit local building control needs notification.Currently rewiring my house. I am installing a new oven - 3.65kW and combi microwave - 3.6kW protected by a 16A mcb.
Would a 2.5mm for each appliance from the cu to a 20A DP switch surffice over a 20m run?
put it on a 32A with 6.0mm cable. that will also future proof it if ever you eant a bigger appliance.Hi All,
Currently rewiring my house. I am installing a new oven - 3.65kW and combi microwave - 3.6kW protected by a 16A mcb.
Would a 2.5mm for each appliance from the cu to a 20A DP switch surffice over a 20m run?
Thanks
thiking 2.5 from cu to dp. 16A is in the manufacture instructions 2.5mm should be sufficient enough just want to make sure!16A looks a bit tight to me. What is the size of the cable from the CU to the DP switch?
was thinking this however most new ovens have a max load of 3.6kW so should be alright to keep it as 2.5mm, 6mm would be overkill, just need someone elses opition.put it on a 32A with 6.0mm cable. that will also future proof it if ever you eant a bigger appliance.
That 16A / 2.5mm is for just one oven/microwave!!!thiking 2.5 from cu to dp. 16A is in the manufacture instructions 2.5mm should be sufficient enough just want to make sure!
[automerge]1600156710[/automerge]
was thinking this however most new ovens have a max load of 3.6kW so should be alright to keep it as 2.5mm, 6mm would be overkill, just need someone elses opition.
I have done the calcs - 16A breaker is acceptacble and thats what the manufacture says.Have you done any calculations?
Or are you looking for a simple yeah, that should be ok.
i will be running 2 seperate circuits for each applianceThat 16A / 2.5mm is for just one oven/microwave!!!
You want two on the same circuit.
You either need two separate 16A circuits or, as above a 6 or 4mm circuit with 32A MCB.
i could run them both off 6mm but want to have them on separate circuits and isolate them individually from the grid switch/CU. And nothing as its my own house.Ah. That’s clearer.
So, new 16A circuit. RCD protected?
What will you do about notification to LABC?
but, you already Have the 6mm circuit. you can run both appliances from that, no new circuit needed!
That doesn't matter. New circuits have to be notified.And nothing as its my own house.
It does not matter if its a Wendy house this part p melarky has been in since 2005 socould run them both off 6mm but want to have them on separate circuits and isolate them individually from the grid switch/CU. And nothing as its my own house.