I'm a in the 3rd year of my C&G 2330 electrical installation course and some time ago I completed a PAT testing course.
I haven't done any PAT testing yet - other than the small amount required on the course.
I have my first job coming up soon - a small engineering firm and I could use a little advice on testing 3 phase appliances.
Is it more or less the same as single phase 230v testing except I need to IR across all 3 phases and earth instead of the one phase and earth?
I've wired a couple of test leads to a couple of probes one on the CPC pin and one on the live so i can probe the plug pins to do the IR test.
Will this suffice or should I invest in an adaptor?
If so, How do the adaptors work? Do they put all 3 phases into the one single phase of the 3 pin plug for the IR test?
Also how long should I advise between tests?
I can't remember much of the course but I want to ensure I carry out all required tests fully.
Any help given would be very much appreciated.
Thanks,
Paul.
Re: 3 phase PAT adaptors
Well for starters - its most important that PAT adaptors for 3 phase equipt. do not allow a mains connection (inadvertantly or not) from the PAT testing equipment. So the first thing you do is snip off the "live" wire from the cable where you're going to terminate it into the adaptor. Next step connect earth (doh !!), then Neutral into first phase conection. Each subsequent phase is then looped together into the first. - see picture I've taken.
PAT testers are configured to apply insulation test voltage to both Live & Neutral, therfore it don't matter the "Live" is snipped off.
All of this is covered in Code of Practice page 76 Para 15.5 notes 4 & 5.
I set my Supernovas up to carry out this test and is listed separately on the test menu.​
Thats fantastic, thanks for the reply and the pictures.
I was going to do the same thing but use the live conductor rather than the neutral.
Thanks again,
Paul.