Phew its been a while since ive been on here (illness) Now I am well again and getting back to work I would like to ask some advice if I may?

When doing a PIR does anyone have a set list of limitations that they put on the form as I do not know how to word the limitations and what you guys put down as your usual limitations such as concealed cables.:angelsad2:

Thanks in advance

ICE
 
Hi ICE welcome back and hope things are improving for you mate.

Have a read of the notes in appendix 6 page 339 and reg 634.2 of the BRB and limitations is something you set up with the client and really is individual to each installation.

The one you highlighted is a good one for domestic installations and yes that would be a normal limitation on nearly every reports SoI

But others might be access to circuits or unable to find circuits. Access might be some circuits that are for production lines that just can not be switched off and so you are limited to what you can do if anything on them, and so you would arrange out of hours working or lim it.

Another common one is Ze, as it is often impossible to completely disconnect an earthing system from an installation safely. So you may do a Ze with it connected and compare notes if you have previous test records, or you will have started a base line level that other test in the future will allude to.

When I quoted for PIRs I did it by the circuit and often on big commercial/industrial sites I would put a time limitation on circuits, ie 30 mins, if I could not identify where/what/how a circuit was going then I would mark that down as a Lim. and either arrange a quote for tracing the circuit on remedial work or it was often as not left.
 
I generally put 'No dismantling or lifting of floorboards' taken straight from the example in the On Site Guide.
 
limitations as per standard list in bs7671(2008)
no Ze due to seals
no I.R. testing between live conductors of lighting circuit
live testing only of circuits affecting trade
no live testing of circuits above 2.5mtr in height
 
Hi ICE welcome back and hope things are improving for you mate.

When I quoted for PIRs I did it by the circuit and often on big commercial/industrial sites I would put a time limitation on circuits, ie 30 mins, if I could not identify where/what/how a circuit was going then I would mark that down as a Lim. and either arrange a quote for tracing the circuit on remedial work or it was often as not left.

Thats a good idea, we have just completed one where we seemed to spend an hour or so on some circuits trying to find where it goes! Agreeing it as a limitation before hand for the time limit could be a cracking plan!
 
is it because they flap their flippers, wanting a fish?
 
why remove main fuse?
 
I usually take the Ze measurment at the feed side of the main switch, with the switch open and the earth conductor disconnected.
 
so do i. can't see why mogga wants to pull the main fuse.
 
could it be that sometimes, and ive come across it myself, the main fuse supplies multiple boards via henley blocks/100a connectors and there is no single main switch
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
PIR Limitations
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
ICE,
Last reply from
Dean Williams,
Replies
13
Views
3,938

Advert

Back
Top