B
Bobster
You spy correctly.
You know there not really suitable for that right?
You spy correctly.
You know there not really suitable for that right?
It is important for the installer to seal all openings into the enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables. See Figure 6.
The intent of the sealing is that, as far as is reasonably practicable, any fire is contained within the enclosure or cabinet and the escape of flames to the surroundings of the cabinet or enclosure or into conduits trunking or ducting is minimised, as intended by Regulation 421.1.201.
How the hell are we meant to infer that from the actual wording of the regulation?
421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
i. have their enclosure manufactured from non-combustible material, or
ii. be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
NOTE 1: Ferrous metal e.g. steel is deemed to be an example of a non-combustible material
NOTE 2: The implementation date for this regulation is the 1st January 2016. This does not preclude compliance with this regulation prior to this date.
It's wide open for the lawyers to argue about.
It would be much clearer if they had also added
iii) All openings to be sealed against the spread of fire
iv) non-flame propagating wiring must be used
v) smoke and/or heat alarm to be installed in vicinity of the consumer unit
vi) fire extinguisher to be located within easy reach of the consumer unit
vii) original installer to check the connections every month at his/her own expense
viii) stop working in domestic premises and leave it to those with less skill and experience
Hello mate, The CU you have used would not be compliant. Needs non combustible cover and blanks see here for Wylex offering; http://www.electrium.co.uk/Wylex_Metal.pdfView attachment 29042
Another piccy. One thing I noticed was the space at the bottom of the breakers where busbar goes is a little tight. So a good idea to remove the din rail with MCBs on it to make sure all bus bar connections are sitting properly. Cannot see in enough if the din rail stays put.
Hello mate, The CU you have used would not be compliant. Needs non combustible cover and blanks see here for Wylex offering; http://www.electrium.co.uk/Wylex_Metal.pdf
if the lid is clossed its not classed as external so it complies acording to leafletThanks for the info fella. The DB in the picture has a metal hinged lid on it out of shot. If the blanking covers need to be metal then so do the MCBs, RCDs and main switch!
if the lid is clossed its not classed as external so it complies acording to leaflet
Used the M40 Wiska sprint glands.
These are good, but bloody expensive at the moment. The price of a new consumer unit keeps on rising, making the domestic market even more fun to get work because the consumer is only concerned with price.
I wonder if the likes of B&Q, Screwfix etc will replace their best selling £50 fully populated high integrity CU's with metal by Jan 2016? Seems unlikely.
I think I'll just hang fire until the 11th hour and see what progression is made.
All seems like over the top nonsense to me at the moment, particularly as non ferrous metal boards have only been suggested as an example.
I wonder if the likes of B&Q, Screwfix etc will replace their best selling £50 fully populated high integrity CU's with metal by Jan 2016? Seems unlikely.
I think I'll just hang fire until the 11th hour and see what progression is made.
All seems like over the top nonsense to me at the moment, particularly as non ferrous metal boards have only been suggested as an example.
These are good, but bloody expensive at the moment. The price of a new consumer unit keeps on rising, making the domestic market even more fun to get work because the consumer is only concerned with price.