Of course it matters which edition it was designed to.
If an installation complies with the edition it was designed to, then as per BS7671 it is not unsafe.
It can’t be unsafe, otherwise the IET would be guilty of promoting unsafe installations.
 
Of course it matters which edition it was designed to.
If an installation complies with the edition it was designed to, then as per BS7671 it is not unsafe.
It can’t be unsafe, otherwise the IET would be guilty of promoting unsafe installations.
A perfect example is the fixing of wiring systems against premature collapse.
Knowing what we know now and following the deaths of firefighters, we can’t now say that an installation which complied to the 16 th edition or the 17th pre amendment 3 are necessarily safe in regards to that particular regulation.
Whether it complied before is irrelevant as we are not inspecting the installation to the date it was designed and installed .
It’s safety must be in regard to the current edition of the wiring regulations full stop.
Obviously if any non compliance’s do not warrant a FI ,C1 or C2 code it can be regarded as satisfactory for continued use but have recommended safety improvements issued to the client.
 
Last edited by a moderator:
A perfect example is the fixing of wiring systems against premature collapse.
Knowing what we know now and following the deaths of firefighters, we can’t now say that an installation which complied to the 16 th edition or the 17th pre amendment 3 are necessarily safe in regards to that particular regulation.
Whether it complied before is irrelevant as we are not inspecting the installation to the date it was designed and installed .
It’s safety must be in regard to the current edition of the wiring regulations full stop.
That’s not a new requirement though is it?
We’ve always been required to install wiring so that it doesn’t present a danger.
All that’s happened, is the IET have addressed poor practices and clarified what is required.
 
That’s not a new requirement though is it?
We’ve always been required to install wiring so that it doesn’t present a danger.
All that’s happened, is the IET have addressed poor practices and clarified what is required.
As far as I’m aware we never had to prevent the wiring throughout the installation collapsing prematurely in the event of a fire.
Cables inside trunking, plastic saddles etc all acceptable as they where In previous editions of the regulations.
No mention of escape routes as that came with the 17 th edition amendment 3.
 
Last edited by a moderator:
The fact that you were unaware that we were required to prevent the premature collapse of wiring systems in the event of a fire, is exactly why the IET decided to clarify the matter.

Every edition and amendment is published 6 months before it comes into force. During those 6 months, we are allowed to design and construct to either edition or amendment.
After the new edition or amendment comes into force, we are still allowed to construct a design which was made before the the new edition or amendment came into force.
There is no time limit on how long after the new edition or amendment comes into force, that we can construct the design.

If anything in the previous edition or amendment were considered unsafe, we would not be allowed to install anything designed to that edition or amendment.
Allowing us to do so would be endorsing unsafe practices.
 
The fact that you were unaware that we were required to prevent the premature collapse of wiring systems in the event of a fire, is exactly why the IET decided to clarify the matter.

Every edition and amendment is published 6 months before it comes into force. During those 6 months, we are allowed to design and construct to either edition or amendment.
After the new edition or amendment comes into force, we are still allowed to construct a design which was made before the the new edition or amendment came into force.
There is no time limit on how long after the new edition or amendment comes into force, that we can construct the design.

If anything in the previous edition or amendment were considered unsafe, we would not be allowed to install anything designed to that edition or amendment.
Allowing us to do so would be endorsing unsafe practices.

Theyre counting on you being competent and taking into consideration consequences of installing to previous editions etc. Come on. You are digging.
 
The fact that you were unaware that we were required to prevent the premature collapse of wiring systems in the event of a fire, is exactly why the IET decided to clarify the matter.

Every edition and amendment is published 6 months before it comes into force. During those 6 months, we are allowed to design and construct to either edition or amendment.
After the new edition or amendment comes into force, we are still allowed to construct a design which was made before the the new edition or amendment came into force.
There is no time limit on how long after the new edition or amendment comes into force, that we can construct the design.

If anything in the previous edition or amendment were considered unsafe, we would not be allowed to install anything designed to that edition or amendment.
Allowing us to do so would be endorsing unsafe practices.
Don’t insult my intelligence please , “the fact I was unaware “
Clutching at straws.
If it was required at the time it would have been in the regulations.
Double pole fusing was once a requirement, how did that one go?
So you must be stating that you’ve always installed wiring systems against premature collapse?
Ever since you’ve been an electrician you’ve always installed metal fixings to hold the cable in place inside trunking?
 
Theyre counting on you being competent and taking into consideration consequences of installing to previous editions etc. Come on. You are digging.
Not at all.
I worked on the Athelete’s village at the Queen Elizabeth Park in Stratford.
Completed in March 2015, constructed to the 16th edition.
 
I'm surprised that the top plate of the CCU has been removed although the hole sizes would be the same and the IP rating when the front cover is replaced fullfills IP4X. Glanding off the SWA is not a problem if it is done before the board is fitted. The SWA is/was used, I presume, with supplementary bonding in place and to aviod the necessity to fit RCDs and also assumes this lnstall was completed before the 18th ed.
Is this really a C2? C3 max and a note regarding the lack of RCDs

Taking all things wrong with the install into consideration i say C2.
Tha angle which swa enters means that the connections are under stress.
Theres alot of dust inside the consumer units due to the large hole. Theres a draft so anything could enter it etc insualtion...
I believe c2 also for the lack of rcd protection due to them being in a commercial premesis and not being used for fridges in all cases also not labelled and no RA.
I stick to my original coding.
 
Don’t insult my intelligence please , “the fact I was unaware “
Clutching at straws.
If it was required at the time it would have been in the regulations.
Double pole fusing was once a requirement, how did that one go?
So you must be stating that you’ve always installed wiring systems against premature collapse?
Ever since you’ve been an electrician you’ve always installed metal fixings to hold the cable in place inside trunking?
I have never, to this day used metal fixings inside trunking to hold cable in place.
Never had the need to.
 